ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat
Recent Posts
Safety at heights?
by gfretwell - 04/23/24 03:03 PM
Old low volt E10 sockets - supplier or alternative
by gfretwell - 04/21/24 11:20 AM
Do we need grounding?
by gfretwell - 04/06/24 08:32 PM
UL 508A SPACING
by tortuga - 03/30/24 07:39 PM
Increasing demand factors in residential
by tortuga - 03/28/24 05:57 PM
New in the Gallery:
This is a new one
This is a new one
by timmp, September 24
Few pics I found
Few pics I found
by timmp, August 15
Who's Online Now
1 members (Scott35), 235 guests, and 27 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
#86812 12/14/03 04:07 PM
Joined: Dec 2002
Posts: 308
E
Edward Offline OP
Member
Can i install a double pole 100Amp breaker into a 125Amp main lug 24circuit panel and call it the main disconnect for that subpanel?
Please give NEC sections.


edward


Thanks
Edward
Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

Joined: Mar 2001
Posts: 2,056
R
Member
408.16(F) permits this type of installation.

Joined: Apr 2002
Posts: 558
C
Member
You need to make sure the loadcenter is listed for using a back-fed main breaker and if so they often will only permit it in a specific location which is designed to accept the required hold down kit. This information should be on the label. Many newer loadcenters are designed to accept main breaker kits that mount in place of the main lugs.

Curt


Curt Swartz
Joined: Dec 2002
Posts: 308
E
Edward Offline OP
Member
Thanks for the reply.
Can i back feed the busbars with a 100Amp breaker and call that the main? Or it has to be a kit that goes in the place of the main lugs?

Edward


Thanks
Edward
Joined: Apr 2002
Posts: 558
C
Member
Yes, you can back feed a breaker in the loadcenter if the instructions on the loadcenter say you can. You are required to secure the back fed breaker so you must purchase a hold down kit that fits the breaker and loadcenter. The hold down kits often will only fit in the one designated position in the loadcenter. If there are provisions to replace the main lugs with a main breaker that is usually the better way to go. Many Square D and GE loadcenters have main breaker kits to replace the main lugs.