#86749 11/29/03 01:27 AM
elecbob Offline OP
A customer has rented space in a single story building with 3 spaces. Each space has 1600 sq. ft. and is seperated by a lathe and plaster wall. His architect says the seperating walls have a 4 hour fire rating and the space can be wired with romex. Any thoughts on this?
thanks
bob
#86750 11/29/03 04:48 PM
I would check with the AHJ for the area.
ed
#86751 11/29/03 07:15 PM
With the exception of an assembly area, you should be fine with type NM cable.
As NEsaprky said, though, check with the AHJ
Ryan Jackson,
Salt Lake City
#86752 11/30/03 09:24 AM
Tom Offline
Also keep in mind that if there will be a dropped ceiling, NM cable would not be allowed above the ceiling as open runs.
#86753 12/01/03 11:41 AM
elecbob Offline OP
I called the AHJ and romex it is. No dropped ceiling but thank you for the reminder.
bob