Member
The NEC does not permit the receptacles in a kitchen, bathroom, or wet bar to be installed Face Up. Are there any products available that will allow a recessed receptacle to be installed that would be flush with the counter when not in use?


Joe Tedesco, NEC Consultant
Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

Joined: Nov 2003
Posts: 269
E
Member
I know it sounds crazy, but what about a floor box?


John
Joined: Oct 2000
Posts: 5,392
S
Member
there was a 'tip out' sort of gizmo posted here once,looked very much a high end deal, i just can't find it. [Linked Image]

the only problem is, kitchen designers won't give most electricians the time of day, i have been party to many a window/counter design here that simply can't meet 210-52.

i'm tired of pissin' in the wind to peole who could care less....

~S~

Joined: Apr 2001
Posts: 4
R
Junior Member
http://www.codecheck.com/images/popupreceptacle.jpg
Does anyone know if these pop-up style receptacles can be approved as suitable for kitchen counters?

Joined: Apr 2001
Posts: 4
R
Junior Member
http://www.codecheck.com/images/IslandBabyBen.jpg Floor boxes (monuments) are a hard sell. Few designers or customers well accept them.

Joined: Aug 2002
Posts: 1,081
T
Member
Redwood Kardon: http://www.codecheck.com

Wow...welcome to ECN.

Joined: Apr 2002
Posts: 7,381
Likes: 7
Member
Redwood:
Welcome to the forum.
Based on the pic only, I cannot give you a firm answer.

IF the item is UL listed/labeled then it should be acceptable in a kitchen. It appears to be mounted in a desk, as I see a phone.

Practically, it may be a tough 'sell', to cut-in to the countertop without a wide choice of decorator trims. Also, drawers would require modifications (depth) to accomodate this item.

I would like more info on this item if possible.

With my AHJ hat on, if an EC could show me a valid UL listing/label, I would accept this device.

John


John