by NORCAL - 03/19/24 05:11 PM
1 members (CoolWill), 250 guests, and 13 robots.
#86716 11/24/03 05:50 PM
Wow, spent the afternoon searching the archives re 100A subpanel. Bazillions of posts, opinions, and interpretations, but no consensus, but the safe way(s) to go are either:
1) Install 90A cb on feeder panel for #4 CU;
or
2) Use #3 CU.
(BTW, I plan on THHN).
Question about option #2- the neutral & grounding bars on the main panel are only rated for up to a #4 CU. What do I do with my grounded & grounding wires if I use #3?
Yes, I've removed the bonding jumper from my sub. Will make sure that neutral bars get only grounded conductors, and grounding bars get only grounding counductors.
Thanks!
#86717 11/24/03 06:41 PM
Tom Offline
Check the manufacturers catalog. Sometimes they make an auxilliary lug that will fasten into a couple of the neutral bus holes. I know that GE and Square D make these for their panels.
