It has been brought to my attention that most EC's will use the push in terminals for plug and switches, instead of terminating conductors around the device screws.
What's your opinion?
I am not an EC.
I have personally seen the effects of push-in terminated devices. (Some of my photos are posted on the board.)
If there is a screw that is used to tighten the connection, such as with the GFCI receptacles (the ones that have a back-stab hole but require the screw to tighten the connection), I don't see a problem.
If one is relying on a spring type of connection, then I would not trust it.
I have also found that the screws provided in some of the cheaper devices are almost as soft as the copper, and are not very sturdy.
If I understand correctly, 12AWG can no longer be used with push-in connections, right? Why is 14AWG permitted and not 12?...
I have done it both ways in the past. And I have to be honest, I have yet to run across a push-in connection that has failed when properly installed. Not to say that it doesn't happen. I have read about others who run across this all the time. I have seen numerous, and I will repeat NUMEROUS, recepticles that failed when the connection came loose from the screw. I have at times used the push-in connection (on 14 awg only) when pigtailing the circuit. I can only assume that the integrety of the connection lies in the ability of the installer. Also, if the device is overloaded the push-in or screw connection will fail. On the cheaper devices they loose tention and overheat with time. Many times I change all the devices in a home because they can't keep anything plugged in. I guess quality lies with the installer.
Blessings,
Mark
I never use a "pushin connection", but do use the back wired devices where the screw clamps a pressure plate against the wire.
Don
Unless it is the type Don describes I will not use them.
About the only place I have ever used the spring type is on a switch as I will know that the current load is low.
I use the screws! I have spent too many hours on service calls troubleshooting loose connections on backstabbed devices.I have also seen the scorched walls and burnt insulation on the wiring from these faulty connections. [Linked Image] My opinion...If the difference in time between backstabbing a device or using the screws, is going to make or break the job, you bid it too low to begin with.
Donnie
The first thing I look for when I get a complaint about no power on a receptacle or a loss of power on a branch circuit is a loose backstabbed connection. 99% of the time I'm right. It was worse before the restriction on wire size to #14, but I always use the terminal screw.
I too use the screws.I've seen several backstabs cause problems.
It doesn't take much more time when you do a few jobs that way.
Russell
I would personally like to thank UL for the continued buisiness i recieve from thier blatant inepptitude
carry on fellas!
~S~
Look here!