1 members (Scott35), 466 guests, and 14 robots.
#86606 11/15/03 10:55 AM
GTE Offline OP
Do ground screws used to to ground metal boxes have to be listed & do they have to be green?
#86607 11/15/03 12:29 PM
No. I think they are very handy to use and I installed my share of them, but they are not a requirement. you do have to bond the boxes (250.148), but in my opinion as long as you do not use a sheet-metal screw, you are fine.
Ryan Jackson,
Salt Lake City
#86608 11/16/03 07:06 AM
Just to add to Ryans answer, for the people that might not of crossed this before.
250.8 prohibits the use of sheetmetal screws for grounding.
#86609 11/16/03 07:28 AM
I will add that many times people get hung up on 250.126 Identification of Wiring Device Terminals.
This article says the ground screws on devices must be green.
Article 100
Device. A unit of an electrical system that is intended to carry but not utilize electric energy.
250.126 has nothing to do with the screws used for grounding anything else.
