#86531 11/08/03 07:09 PM
Joined: Jan 2002
Posts: 64
R
Rabbit Offline OP
Member
Is it a violation to bring a raceway into the side of an outdoor disc. above the fuses? If it is I can't find it, and have never been failed for doing it. [Linked Image]

Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

#86532 11/08/03 07:13 PM
Joined: Aug 2003
Posts: 1,374
R
Moderator
It should be fine if you are using sealing locknuts to maintain the integrity of the NEMA 3R enclosure rating.


Ryan Jackson,
Salt Lake City
#86533 11/08/03 07:34 PM
Joined: Jan 2002
Posts: 64
R
Rabbit Offline OP
Member
Yes I agree. Had a little disagreement with a coworker regarding this. He claims it is the reason manufactuers don't supply KO's in this location.

#86534 11/08/03 07:37 PM
Joined: May 2002
Posts: 1,716
R
Member
Hey Rabbit, I agree with Ryan with a foot note. Some manufacturers will leave you hanging due to their listing info regardless of the entrance fittings.

I have never been tagged for this.

How was the antique tractor show? I ended up working on a MG set that weekend and the next. [Linked Image]


Roger

#86535 11/08/03 07:51 PM
Joined: Aug 2003
Posts: 1,374
R
Moderator
I think the "thats why theres no KO's" is a pretty cheesy argument.

What about a typical indoor 42 circuit can that has no KO's? Does he say that you can't punch it out? Of course you can.

[This message has been edited by Ryan_J (edited 11-08-2003).]


Ryan Jackson,
Salt Lake City
#86536 11/08/03 07:52 PM
Joined: Mar 2003
Posts: 92
G
Member
Ryan J. , I have never heard of a sealing locknut. Could you reference a code article and maybe a link to a picture of one? Also are these required for type 3R enclosures?

#86537 11/08/03 08:06 PM
Joined: Jan 2002
Posts: 64
R
Rabbit Offline OP
Member
Hey Roger,

Danged if I know I wound up working too. I had built a service for a manufacturd building (spelled double-wide) and when the AHJ came to look at my service he wouldn't accept the NM inside. This is being used for a pharmacy. The owner freaked and I wound up Jerking MC all day Saturday. There's always next year.

#86538 11/08/03 08:06 PM
Joined: Aug 2003
Posts: 1,374
R
Moderator
This is a sealing locknut:
[Linked Image from iguana18.securesites.com]

[This message has been edited by Ryan_J (edited 11-08-2003).]

I'm looking for the code right now....I think 110.3(B) might apply, but there is an article that states something to the efect of "equipment shall be deemed suitable for the enviroment in which it is installed", and I beleive there is somewhere else, but I'm struggling to find it! Help please?

[This message has been edited by Ryan_J (edited 11-08-2003).]


Ryan Jackson,
Salt Lake City
#86539 11/08/03 08:30 PM
Joined: Jan 2003
Posts: 4,391
I
Moderator
I just had to use some of these in 4" a real bear to put on. [Linked Image]


Bob Badger
Construction & Maintenance Electrician
Massachusetts
#86540 11/08/03 08:57 PM
Joined: Jul 2002
Posts: 680
W
Member
Why couldn't you use a myers hub?? way better than a sealing locknut IMHO