Hello everyone, I was wondering if anyone had any idea on where I can get a CT for a 3000 amp service. I'm trying to monitor the KWH consumption for my facility and the largest CT I can find is a 2000 amp. Maybe if no one knows of any CTs that big they can give me some info on how I might accomplish my goal. These pulse inputs are going back to a monitoring device called a gateway which can be accessed anywhere through a modem. Thanks for any help. Chris
|
|
|
|
Joined: Mar 2001
Posts: 2,056
Member
|
Could you monitor one of a parallel group and have your software multiply the results by the number of conductors? (Forgive my ignorance)
|
|
|
|
Joined: Jul 2001
Posts: 599
Member
|
Check out a company called Flex-Core at http://www.flex-core.com. They make all sorts of different CTs, including split core styles for mounting on existing cables. Square D also lists window style units up to 6000:5 ratios and split cores to 5000:5
|
|
|
|
Joined: Apr 2002
Posts: 3
Junior Member
|
Chris,
Most CT's will have a "rating factor" (RF). For instance, if the CT was a 2000 amp unit with an RF of 2, then the thermal capability would be 4000 amps.
Because of this, it is not always necessary to "match" the CT size to the service size.
Feel free to email me if you have more questions.
Bob
|
|
|
|
Joined: Jul 2001
Posts: 599
Member
|
While bgautreau is technically correct concerning "rating factor", you must still take into account your transformer ratio.
In your case a 2000:5 CT is a 400 to 1 ratio, so when it is used on a 4000A service it will provide an output of 10A. Your measuring equipment may not be able to deal with this large of a value.
The rating factor should only be used to allow for momentary overcurrents (i.e. motor start-up)which do not need to be be measured accurately
|
|
|
|
Joined: Apr 2002
Posts: 7,383 Likes: 7
Member
|
Try National Meter Industries www.national-meter.com or 1-800-325-6674 They have any ct's and are very helpful John