0 members (), 373 guests, and 12 robots.
#86048 09/03/03 10:59 AM
boxford Offline OP
What article in the NEC states that you can only utilize a circuit breaker up to 80% of its capacity?
#86049 09/03/03 11:33 AM
Ron Offline
210.19(A)(1) & 215.3 provide limits for overcurrent protection of continuous loads
Ron
#86050 09/04/03 09:41 AM
(1999) 384-16(d) - Continuous Load
'The total load on any overcurrent device located in a panelboard shall not exceed 80% of its rating where, in normal operation, the load will continue for 3 hrs. or more.'
(2002) - In 2002 this section was deleted.[Proposal 9-107, ROP] It was contended that rules in 210.19(A), 210.20(A), and 215.3 cover this issue and this wording was unnecessary.
#86051 09/04/03 12:46 PM
boxford Offline OP
Thank you very much I really appreciate it.
#86052 09/12/03 08:35 AM
Most small molded-case breakers are only rated for 80% of their nominal rating. Larger frame molded case breakers can be specified as "100% rated" but will cost more. Best to check with the manufacturer.