ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat
Recent Posts
UL 508A SPACING
by ale348 - 03/29/24 01:09 AM
Increasing demand factors in residential
by tortuga - 03/28/24 05:57 PM
Portable generator question
by Steve Miller - 03/19/24 08:50 PM
Do we need grounding?
by NORCAL - 03/19/24 05:11 PM
240V only in a home and NEC?
by dsk - 03/19/24 06:33 AM
New in the Gallery:
This is a new one
This is a new one
by timmp, September 24
Few pics I found
Few pics I found
by timmp, August 15
Who's Online Now
1 members (ale348), 302 guests, and 14 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
Page 1 of 2 1 2
#85935 08/21/03 02:31 PM
Joined: Apr 2002
Posts: 197
T
triple Offline OP
Member
The last sentence of 422.10(A) allows the branch circuit of even a single household range to be sized according to table 220.19. I used to think that table (and section of the code) were only meant to be used for service load calculations. In essence, a single range rated at 75A (according to the marking on unit) can be hooked up with 50A wire and have 50A OCP. I realize that rarely is the unit going to be operated at full load but why is this allowed? It is like hooking up a group of motors and ignoring a couple dozen FLA’s just because "rarely" will all motors be used at once. Are the numbers listed on ranges overly optimistic on how much draw they have or what?

Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

#85936 08/21/03 04:00 PM
Joined: Sep 2002
Posts: 1,498
Likes: 1
C
C-H Offline
Member
If you weren't designing like this, you would end up with huge wires and an 80A OCP. The range heats up pretty quick, and the load falls after that: Either the thermostats or the user turns the oven and rings down.

Sure, you could overload the circuit: Keep the oven open and boil water on all rings. You will have to replace the boiling water with cold water at regular intervals. The kitchen will be lika a sauna. To damage the wiring, not just tripping the breaker, you will have to keep doing this for quite some time.

#85937 08/21/03 11:52 PM
Joined: Apr 2002
Posts: 197
T
triple Offline OP
Member
The wire has absolutely no risk of being damaged. The OCP is sized for the wire and will protect it. That is not what my concern is. My point is, in most any other circumstance, if a piece of equipment has a nameplate current rating of "X" amps, how can the NEC dictate some lesser rating? Please refer to my motor example and explain the difference. I also have a more direct question. If a range has a tag, which says it will draw 75A at full load does it actually draw that much with all elements on? If so, how can a 50A breaker hold this load? It is very conceivable that a person cooking for a large group (perhaps a family get-together) will use all four burners and the oven at the same time. Will the OCP allow such an action dependably? If I just had my new range installed and properly wired up by a licensed electrician, I would be VERY upset if the code allowed my breaker to trip! I am led to believe that the VA's listed on ranges must be quite inaccurate or 220.19 would not be used for branch circuits. To be clear, I totally understand 220.19's use for service load calculations. Using it to size the wire and breaker for a single range in a household seems to go against everything else in the code book!

#85938 08/22/03 01:12 AM
Joined: Jun 2003
Posts: 681
P
Member
Triple
when refering to 220.19 from 422.10, there is a note # 4. Did you read this note? Maybe it will help clear this up for you.

Pierre


Pierre Belarge
#85939 08/22/03 01:16 AM
Joined: Jun 2003
Posts: 681
P
Member
When I prepare guys for taking the test, I point out that in Part II of Article 220, Note 4 to Table 220.19 is for branch-circuit loads, the rest of Part II is for Feeders and Services.

Pierre


Pierre Belarge
#85940 08/22/03 03:43 PM
Joined: Sep 2002
Posts: 1,498
Likes: 1
C
C-H Offline
Member
Quote

If a range has a tag, which says it will draw 75A at full load does it actually draw that much with all elements on? If so, how can a 50A breaker hold this load?

To get 75A you will have to turn on everything at the same time. Having everything turned on at the same time isn't enough, since the oven will have a low current draw once it is warm.

Most, if not all, types of overcurrent protection allows a current exceeding the rating for a limited period of time. The wires will take a significant time to become warm. Ordinary breakers have a thermal element that heats up, just like the wires. When it gets too hot, the breaker trips.

Without access to trip curves for American breakers, I can't give you any exact figures. But I would guess that you can take out about 125% of the capacity for half an hour or more. For a few minutes, I'd expect the breaker to allow 150%.

Remeber that you are starting with the breaker cold when you turn on the range to get the maximum load.

Quote

If I just had my new range installed and properly wired up by a licensed electrician, I would be VERY upset if the code allowed my breaker to trip!

I on the other hand would be upset if the electrician oversized the wiring, since it costs me money. There are other things in life to spend money on than wire. I don't mind the breaker tripping sometimes. Even if it trips once a week, it will take a century or so before it wears out.

#85941 08/22/03 03:55 PM
Joined: Jan 2003
Posts: 4,391
I
Moderator
C-H

I can think of no time that the NEC allows us to intentionally use a breaker smaller than the load served.

Most times we must wire for 125% of the nameplate current.

I do agree the breakers will allow higher than the marked rating for a period of time, but the NEC does not.

As far as over sizing circuits I think this is common in the NEC.

When you do a service calculation per NEC you come up with a much larger service than the POCO knows you need.

Bob




[This message has been edited by iwire (edited 08-22-2003).]


Bob Badger
Construction & Maintenance Electrician
Massachusetts
#85942 08/22/03 04:08 PM
Joined: Apr 2002
Posts: 197
T
triple Offline OP
Member
Yes, I had read note 4 to the table before posting this topic. I understood WHAT the code was saying but I didn't understand WHY. Where else in the code is this type of potential overloading allowed?

#85943 08/22/03 10:14 PM
Joined: Apr 2002
Posts: 558
C
Member
triple

The heating elements in ranges are constantly turning on and off. For the cooktop portion this is controlled by the hi-low control. If you turn the control to low it turns the element on for a short time and then off for a long time then back on for short time to maintain the low temperature. If you set the control to hi it will turn the element on for a longer period of time then off for a short time then back on. The over element runs the longest time during the initial heat up of the oven but after that it normally is only on for very short periods of time. If you were to measure the load on a range circuit the only time you would ever see it draw the nameplate rating is if the oven and all burner elements were turned on from a cold start but this would only last a very short time before the elements started cycling on and off.

A perfect example of where the NEC permits loads in excess of the branch circuit conductors ratings would be for welders (Article 630)

Curt


Curt Swartz
#85944 08/23/03 10:59 AM
Joined: Jan 2003
Posts: 4,391
I
Moderator
OK, you got me with the welders [Linked Image] I had forgotten about those.

But welders are one of the items listed in Table 240.4(G) "Specific Conductor Applications", I see nothing about ranges or appliances.

You are right that the load is not continuous but other than welders I can not think of a place you can undersize conductors and breakers.

Motors can have a larger breaker than the conductor is rated for but the conductors still must exceed the load.

I will keep an open mind here as I have been wrong before and I can always learn something new. [Linked Image]

Bob


Bob Badger
Construction & Maintenance Electrician
Massachusetts
Page 1 of 2 1 2

Link Copied to Clipboard
Powered by UBB.threads™ PHP Forum Software 7.7.5