#85842 08/11/03 09:53 PM
Redsy Offline OP
A UF cable to a lamppost must be sleeved through the concrete in order to comply with 340.12 (8).
Correct?
Not according to the installation instructions.
#85843 08/12/03 08:05 AM
GEO Offline
Redsy
which instructions? GEO
#85844 08/12/03 09:03 AM
Redsy Offline OP
The installation instructions included with the lamppost show a cable routed through the hole in the bottom/side of the post and then concrete being poured in the hole.
#85845 08/12/03 11:37 PM
Redsy,
Do the Instructions mention concrete?
#85846 08/13/03 07:04 AM
Redsy Offline OP
Bill, Geo,
Yes, the installation instructions show concrete being poured around a cable which enters the post.
#85847 08/13/03 07:43 AM
GEO Offline
REDSY
was it made in china and sold at home DE pot?
OOPS i never did that i think.
#85848 08/13/03 09:03 AM
Lemme guess...the instructions have something along the lines of "Must be installed in accordance with local codes by qualified personnel..." which translates to "Loophole."
#85849 08/13/03 09:16 AM
Redsy,
Can you scan the instructions and send it to me?
How about writing them a letter and asking them to explain? What do you think?
[This message has been edited by Bill Addiss (edited 08-13-2003).]
#85850 08/13/03 01:11 PM
Redsy Offline OP
I will probably be asked to install it within a few days.
I'll double check the instructions and try to remember to keep them.
#85851 08/13/03 05:53 PM
Tom Offline
I guess this is one of those cases where following the instructions will get you in trouble.
Uses Not Permitted- 340.12(8) Embedded in poured concrete...