#85604 07/21/03 07:33 PM
Joined: Jan 2002
Posts: 324
A
Member
This was asked to me today by another electrical contractor. If a person uses a 120v photocell to break one leg of 240v sign circuit would this be a code violation as long as the ocpd is a double pole? Of course we agreed that a 240v photcell should be used in this situation to de-energize the sign for safety. Any thoughts or code references?

Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

#85605 07/21/03 09:04 PM
Joined: Apr 2002
Posts: 7,381
Likes: 7
Member
THe bible is in the truck, so I'll give an opinion.
THe photocell is more than likely not being used according to mfg instructions, if it's rated 120 volts.

Breaking one leg is not a good practice, and leaves an energized conductor somewhere btwn the PC and the sign. A sign tech may think the sign is de-energized. This is similar to using a single pole t'stst (line volt) to control a 240 volt bb heater; or a s/p switch to "shut-off" a 240 volt circuit.

"It works, don't it????"
(Famous last words.
John


John
#85606 07/21/03 09:47 PM
Joined: May 2001
Posts: 552
T
Member
A 240 volt photocell only breaks 1 phase of the circuit anyway? At least, that is all that I have ever seen.

[Linked Image from pages.sbcglobal.net]


Donnie
#85607 07/21/03 09:52 PM
Joined: Apr 2002
Posts: 558
C
Member
The only difference between a 120 volt photo control and a 240 volt photo control is the heater voltage. If you use a 120 volt control you will need a neutral for the control but if you use a 240 volt control the white wire from the control is connected to the other leg of your circuit and a neutral is not needed. Standard photo controls will only switch one leg of your circuit. I have never seen a 2-pole control.

Curt


Curt Swartz
#85608 07/21/03 09:54 PM
Joined: Apr 2002
Posts: 558
C
Member
I was just going to look for a diagram to post but it looks I was too slow.


Curt Swartz
#85609 07/21/03 10:57 PM
Joined: Jan 2002
Posts: 324
A
Member
Thanks for the input, I did not know that a 240v photocell only broke one leg. I would have thought it worked as a double pole switch. Thanks

#85610 07/22/03 08:43 AM
Joined: Jun 2003
Posts: 681
P
Member
arseegee
I thought like you did. I just called a supplier and he checked 2 different photocell manufacturers. Both showed only one leg being opened. You learn something new everyday!

Pierre


Pierre Belarge
#85611 07/22/03 04:03 PM
Joined: Apr 2002
Posts: 2,527
B
Moderator
May be worth mentioning that there is a significant difference between control and disconnecting means. A photocell does the first taskā€”it is suicidal to assume it is always intended to do the second.

#85612 07/23/03 07:44 PM
Joined: Apr 2002
Posts: 7,381
Likes: 7
Member
Learned something topday, and I agree wholeheartedly with Bjarney!!
John


John