would a fire switch (disconnect before meter)
be wired as the main disconnect for the service? thanks GEO

Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

#84695 04/24/03 02:13 PM
Joined: Nov 2000
Posts: 2,148
R
Member
Geo,
The only problem is that 230.91 requires that the service OCPD be a part of or be located immediately adjacent to the disconnect.
Don


Don(resqcapt19)