Can someone help clear up what I do with the LRC once I figure it out using Tables 430-151(A) and (B) and add it to the remaining loads to to obtain the an equivalent LRC for the combined load, as paragraph #3 has me do?

430-110(c)(2) says to size the disco means at 115% of the sum of all currents at the full load condition, which I do according to the second paragraph of 430-110(c)(1).

Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

#84691 04/23/03 08:08 AM
Joined: Mar 2001
Posts: 2,056
R
Member
Uh-oh, let me try again:

The first paragraph is used to back-calculate a HORSEPOWER rating for the disconnect by utilizing the LRAs.
The second paragraph ensures that the AMPERE rating of the chosen disconnect doesn't fall below 115% of FLAs.

Ex: 460 Volt 3 phase motors

2 5HP Motors @ 46 LRA each, and 7.6 FLA each
1 10 HP Motor @ 81 LRA, and 14 FLA
Total LRA 173 Amps
Total FLA 29.2 Amps
Total 203.2 Amps

Ref Table 430.151 (B) = 30 HP rating (218 amps max.)

30 HP Disconnect is acceptable, provided it has a 33.58 amp or greater rating.
(29.2 x 115% = 33.58 amps.)