#84677 04/20/03 09:31 PM
Joined: Nov 2002
Posts: 558
G
Member
I need some help guys. I got into a friendly argument with an EC friend of mine about sizing subfeed conductors. House has 200a MB 40 space panel,adding 100a breaker to feed 100a MB panel in detached garage.I say the feeder wires must be sized using 310.16. He says you can use table 310.15(B)(6). Who eats the crow sandwich? Russell

Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

#84678 04/20/03 09:59 PM
Joined: Apr 2002
Posts: 558
C
Member
Table 310.15(B)(6) Is for the service entrance conductors, service lateral conductors, and feeder conductors that serve as the main power feeder to a dwelling unit. A garage is not a dwelling!

Curt


Curt Swartz
#84679 04/20/03 10:17 PM
Joined: Feb 2003
Posts: 169
R
Member

#84680 04/20/03 10:44 PM
Joined: Nov 2002
Posts: 558
G
Member
Ok,this means that no subpanel fed from this 200a panel in the house could be fed with the reduced wire sizes in 310.15(b)(6). This includes subpanels inside the house itself, correct? Thanks for your replies! Russell

#84681 04/21/03 07:05 AM
Joined: Mar 2001
Posts: 2,056
R
Member
Have him read 310.15(6).
See if he still disagrees.
I,ve seen this mistake several times.
The easiest thing might be to install a smaller feeder breaker (80-90 amp?), if the load permits it.

#84682 04/22/03 08:54 PM
Joined: Feb 2001
Posts: 308
S
Member
When the code allowing downsizing the wiring to feed the dwelling unit was submitted, I believe the data used to support this was utility actual power usage from monthly meter readings. (Please correct me if I'm wrong on this anybody.)

Since the feed to garages is not metered and thus not included as part of the data, garages are not allowed to use this table, only the feed for the house.