ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat
Recent Posts
Safety at heights?
by gfretwell - 04/23/24 03:03 PM
Old low volt E10 sockets - supplier or alternative
by gfretwell - 04/21/24 11:20 AM
Do we need grounding?
by gfretwell - 04/06/24 08:32 PM
UL 508A SPACING
by tortuga - 03/30/24 07:39 PM
Increasing demand factors in residential
by tortuga - 03/28/24 05:57 PM
New in the Gallery:
This is a new one
This is a new one
by timmp, September 24
Few pics I found
Few pics I found
by timmp, August 15
Who's Online Now
1 members (Scott35), 223 guests, and 26 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
#84673 04/20/03 11:54 AM
Joined: Feb 2001
Posts: 308
S
Steve T Offline OP
Member
Does anyone know if there is a requirement for identifying multi-wire branch circuits in the panel. If not it seems to me there should be. It can be very difficult for the next electrician to properly modify breaker spaces if need be without knowing which neutral goes with which hots.

Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

#84674 04/20/03 03:03 PM
Joined: Feb 2002
Posts: 840
C
Member
No requirement. That's just one of the challenges of being an electrician, I guess.


Peter
#84675 04/21/03 09:13 AM
Joined: Oct 2001
Posts: 597
E
Member
I understand the concern. As a regular practice, on raceway systems, I group the neutral with its related phase legs and use a wire tie or, at minimum, tape to identify the group, close to the raceway entry to the panel (assuming more than one neutral is in the raceway). If I have to verify neutral - phase leg combinations on an existing panel as part of the changes I'm doing, again, I'll mark the multiwire group with wire tie, etc., so as not to have to duplicate my effort the next time.

Al


Al Hildenbrand
#84676 04/26/03 08:29 PM
Joined: Feb 2001
Posts: 159
C
CRW Offline
Member
I feel it's always a good idea to put a wire number marker on both the phase conductor and the associated neutral. If the neutral is shared, put both or 3 numbers on it. This is good practice especially for conduit systems, but also for cables (NM, MC) as well. You never know when you may have to move a wire around, and why not make it as easy as possible to identify it?


Link Copied to Clipboard
Powered by UBB.threads™ PHP Forum Software 7.7.5