Does the NEC specifically state that service conductor shall be USE or SE cable? If so, please state article number. Thanks
Stay up to Code with the Latest NEC:
>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides
Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep
>> 2020 NEC & Related Reference & Study Guides
#84597 04/14/03 11:52 AM
Individual Service Conductors in raceways may be of a type that is suitable for environment encountered (usually wet locations). As far as cables such as NM or UF, their specific articles (334.12, 340.12, respectively) state that they are not permitted to be used a service-entrance cable.
#84598 04/14/03 08:24 PM
See also 230.43
#84599 04/18/03 02:31 PM
see also 310-15(b)(6)