ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat
Recent Posts
Increasing demand factors in residential
by gfretwell - 03/28/24 12:43 AM
Portable generator question
by Steve Miller - 03/19/24 08:50 PM
Do we need grounding?
by NORCAL - 03/19/24 05:11 PM
240V only in a home and NEC?
by dsk - 03/19/24 06:33 AM
Cordless Tools: The Obvious Question
by renosteinke - 03/14/24 08:05 PM
New in the Gallery:
This is a new one
This is a new one
by timmp, September 24
Few pics I found
Few pics I found
by timmp, August 15
Who's Online Now
0 members (), 255 guests, and 16 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
Joined: Dec 2002
Posts: 308
E
Edward Offline OP
Member
I donot have a 1990 code book can somebody check to see if GFCI was a requiremnt for replacing two prong outlet.(without EGC)

Thank you
Edward


Thanks
Edward
Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

Joined: Feb 2002
Posts: 2,233
H
Member
Yes, as per 210-7 (d) exception in the 1990 NEC book on page 70-35.

Joined: Oct 2000
Posts: 4,116
Likes: 4
Member
Edward,

1990 NEC 210-7(d)Ex. allows a GFCI Receptacle to replace a 2 prong receptacle where a grounding means does not exist.

Bill


Bill
Joined: Oct 2000
Posts: 4,116
Likes: 4
Member
Harold,

I guess you type faster than I do!

[Linked Image]
Bill


Bill
Joined: Oct 2002
Posts: 70
B
Member
Guys,

Don't have a 90 NEC, but I believe it does not "require" a GFCI but "allows" it.

Bob

Joined: Oct 2000
Posts: 4,116
Likes: 4
Member
Bob,

I did say "allows", but if a 3 prong receptacle is to be installed where there is no grounding means, GFCI protection is required.

[Linked Image]
Bill

[This message has been edited by Bill Addiss (edited 04-12-2003).]


Bill
Joined: Oct 2002
Posts: 70
B
Member
Bill,
You said "allow", Edward said "requirement", but you are right on the GFCI if you go to 3 prong and don't provide a ground.

How do you get that smiley in the text body?

Bob