412
11
I donot have a 1990 code book can somebody check to see if GFCI was a requiremnt for replacing two prong outlet.(without EGC)
Thank you Edward
Thanks Edward
Yes, as per 210-7 (d) exception in the 1990 NEC book on page 70-35.
Posts: 4,116 Likes: 4
Edward,
1990 NEC 210-7(d)Ex. allows a GFCI Receptacle to replace a 2 prong receptacle where a grounding means does not exist.
Harold, I guess you type faster than I do! Bill
Guys,
Don't have a 90 NEC, but I believe it does not "require" a GFCI but "allows" it.
Bob
Bob, I did say "allows", but if a 3 prong receptacle is to be installed where there is no grounding means, GFCI protection is required. Bill [This message has been edited by Bill Addiss (edited 04-12-2003).]
Bill, You said "allow", Edward said "requirement", but you are right on the GFCI if you go to 3 prong and don't provide a ground.
How do you get that smiley in the text body?
Bob
Curt Swartz
