466
14
A light fixture is supposed to be 8' high and 3' out from the top of the bath tub. I assume this applies to ceiling fans too, correct?
Just to be politically correct, these fixtures would have to fit the descriptions given.(cord connected, hanging, lighting track, pendants, or as you mentioned ceiling suspended fans.
Russ
What do you do if 3' out from the tub puts you up against the opposite wall of the bathroom?
TW
Trainwire, you would have to use a recessed fixture listed for the application.
Ah, I think I understand,
The fan/light/heater/nightlight that's stuck up into the cieling is ok.
TW
Posts: 4,116 Likes: 4
Is a standard ceiling-mounted fixture considered a "Hanging Fixture" as prohibited in 410.4(D) ?
Inspectors?
I don't think 410.4(D) applies to surface mounted wall or ceiling fixtures. If it does apply to surface mounted fixtures it would also apply to recessed fixtures since there aren't any exceptions. The Handbook states that recessed and surface mounted fixtures are acceptable within this zone.
Curt
Curt Swartz
Curt,
I agree that surface-mounted fixtures are permitted, and have never personally heard any AHJ objections to them, but I think we've got some differing opinions on that here.