#84402 03/27/03 10:00 PM
Joined: Feb 2003
Posts: 13
B
Member
I am Installing an 800 amp service 480v 3-phase from a 480/277 wye Utility transformer The service is for 3 phase motors only and I am paralleling 3 350kcmill conductors. I believe I am correct on pulling a 1/0 grounding conductor although after looking at an identical job 3/0 was used. Am I OK? Also am I right that from the transformer to the 1st disconnect this would be considered a neutral and be taped white and at the 1st disconnect where I am bonding with the grounding electrode conductor afterwards it would be a green ground?

Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

Joined: Feb 2003
Posts: 169
R
Member
250.66 2/0 copper or 4/0 alum.

Yes from the Main Disconnect on, the neutral is not required if the circuits are not useing it. A equipment ground is required 250.118 and 250.122.

Russ

Joined: Mar 2003
Posts: 15
B
Member
By looking at T250.66 the previously given interpretation is incorrect. The left side of the table states the size of largest ungrounded service-entrance conductor or equivalent area for parallel conductors. Since you are using 3-350kcmil the equivalent area will be over 1100 so you would want to use a 3/0 copper.

Joined: Jan 2003
Posts: 26
J
Member
I am just wondering myslef, If you go to table 310.16 using col. two, 350 kcmil is good for 310 amps
310 time 3 = 930 amps.

Also 350 kcmil times 3 = 1050

if we then go to Table 250.66 and rea Over 600 through 1100 it says to us 2/0 copper.

I would say that's how I would figure it out.


Joe Rossi
Joined: Mar 2003
Posts: 15
B
Member
Table 250.66 states equivalent area for parallel conductors. Just because it says 350kcmil does not mean that the equivalent area of that conductor is 350. If we reference Ch. 9, Table 5 it goes in depth on what the specific areas are for various insulated conductors. So depending on what insulation is being used, that will determine what the equivalent area is for the parallel conductors. I went through the calculations of a few of the insulations and made an educated decision that under most circumstances, if not all, the equivalent area of 3 - 350 would be greater than 1 - 1100 of the insulation being used. I hope that answers where I am coming from.

Thanks,
Brian

Joined: May 2001
Posts: 552
T
Member
The insulation thickness has nothing to do with the kcmil of the copper.Use chapter 9 table 8.

Table 250.66 note 1 applies.
350 x 3 =1050 would require 2/0 copper

[This message has been edited by txsparky (edited 03-28-2003).]


Donnie
Joined: Feb 2003
Posts: 13
B
Member
I am still confused. Also I could of gotten away with 300mcm but I had 350 to use up. Im not sure if I mentioned that I am parrelling 3-350's in 3 different conduits. For the grounded conductor (from the transformer to the main disconnect). I used 1/0 becuase of 250.24B2. For the equipment grounding conductor (from the main breaker to my Motor Stater Panel) I used 1/0 becuase I have an 800 amp breaker going off of table 250.122 Please tell me if I am wrong and thank you for the prevois replys.

Joined: May 2001
Posts: 552
T
Member
The EGC from the disconnect to the motor starter panel is based on 250.122.

The GEC for the service is based on 250.66



[This message has been edited by txsparky (edited 03-28-2003).]


Donnie
Joined: Feb 2003
Posts: 13
B
Member
My grounding electrode conductor from my ground rod to my service equipment is sized from 250.66. 250.66A not required to be larger than 6 copper although I made it 1/0 also. My equipment grounding conductor from my main breaker to my starter enclosure is 1/0 according to TBL250.122 So from My Main Breaker to the Utility Trasformer Are my grounds considered a grounded conductor brought to service equipment? (under 250.66 FPN says see 250.24B) If so wouldnt it be sized based on the size of the ungrounded service-entrance conductor in each raceway according to 250.24B2 for parallel conductors? Or am I confused and my GEC has to be ran clear back to the transformer also?

Joined: Feb 2003
Posts: 138
W
Member
BiggladAnt,

If I understand your system correctly;

You pull 3-350 phase conductors and a 350 grounded conductor in each conduit(based on a wye xfr., the grounded conductor (neutral) is derived from the xo post on the xfr).

From your first means of disconnect, you would bond the grounded conductor (neutral) to the enclosure. You then need to install a grounding electrode and grounding electrode conductor. The GEC that runs to the grounding electrode needs to be sized at 3/0.
However, that does not mean the ground rod. The ground rod only needs a 6ga. conductor. The other grounding electrode needs the 3/0 run to it. The other electrode would be the water pipe within 5 feet of the entrance of the building or the structural steel. Much confusion is due to many of us thinking of the ground rod as THE grounding electrode.

Hope this helps!

Dave

[This message has been edited by WebSparky (edited 03-28-2003).]


Dave