Can I use a male plug on romex (NM-B) cable......legally? Thanks for your information.
If I knew it all....I wouldn't be here asking!!
|
|
|
|
Joined: Aug 2002
Posts: 1,691
Member
|
No. I believe cord caps are only listed for flexible temporary cords.
|
|
|
|
Joined: Mar 2003
Posts: 3
OP
Junior Member
|
Thankyou so much for your help on this. I'm by no means an electrician......but I've seen this dozens and dozens of times, even in my old job (OSHA), and I know I cited this, but I had a client give me a fit today, and I just couldn't remember how I had cited this!!!! Any NEC to go with this would be GREATLY appreciated. First time posted on this board......This is one of the most impressive things I've ever seen on the internet!!!! Again, thankyou sooo much See ya' Brian
If I knew it all....I wouldn't be here asking!!
|
|
|
|
Joined: Oct 2000
Posts: 5,392
Member
|
This would be a rating/listing issue, however i would like to know if there is a male cord cap that is applicable to 527.4(C) ex. out there?
|
|
|
|
Joined: Apr 2002
Posts: 2,527
Moderator
|
It’s likely that wire terminations in cord caps are intended/listed for solid conductors.
|
|
|
|
Joined: Aug 2002
Posts: 1,691
Member
|
Bjarney
I was in a lighting section of a department store last year here in New York's Chinatown and noticed that the receptacle bar (those Wiremold raceway things) that all the table lamps were plugged into was terminated in a length of AC ending with an armored heavy-duty cap (you know the ones with the grounded metal husk on them).
Needless to say it gave me the willies...especially if the end of the AC going into the plug didn't have a little "Red Devil" to protect the wires. Scrape...scrape....KA-POOF!!
Passing by some construction sites, I've seen Romex hooked up to cord caps, usually the square yellow plastic ones.
What makes me say "no" to this is common sense.
I mean...stop and think about it for a second:
The terminal screws inside a plug are small and there's not enough space to properly bend a stiff solid wire around them, so what you might have is a little stump of conductor clamped under a screw. I guess that could lead to overheating....
Also, since the insulation on AC or NM is so stiff, the cap's strain relief (if it has one) doesn't have anything to "bite" on. There's practically no "give" so the wire can also break inside the plug's housing, dance around eventually short something out in there.
Please note that these are not scientific observations, just common sense from what I've seen.
Disclaimer: I am NOT an electrician, so I tend to err on the side of caution. Also, the instruction sheets packed with some heavy-duty plugs and connectors I've used say it is to be used only with flexible cord - type X and wire gauge size Y.
[This message has been edited by SvenNYC (edited 03-26-2003).]
|
|
|
|
Joined: Apr 2002
Posts: 2,527
Moderator
|
There was a recent photo posted at E-C.net picturing {3?} NM cables with cord caps—that may have been found above a suspended ceiling, ostensibly powering lay-in fluorescent fixtures.
|
|
|
|
Joined: Jan 2002
Posts: 163
Member
|
UL gives little information about conductors for 'attachment plugs' - category AXGV in their Green Book - however, as there are so many different types of plugs it seems to indicate the mfr. would give specific information about the types of conductors/cords acceptable for use with a particular plug.
|
|
|
|
Joined: Mar 2003
Posts: 47
Member
|
STILL LOOKING-- but for now you purchase a cord cap not romex cap GEO must be approved for the use ul white book states FLEXIBLE cords or cable romex protected, supported, etc.etc etc---- WILL NOT ACCEPT and it looks ulgy too
[This message has been edited by GEO (edited 03-26-2003).]
|
|
|
|
Joined: Aug 2002
Posts: 1,081
Member
|
|
|
|
Posts: 524