#84345 03/19/03 05:35 PM
Joined: Mar 2003
Posts: 92
G
gserve Offline OP
Member
Is 3 90 degree and 2 offset bends at boxes in 1 run from box to panel code complient? (EMT)

Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

#84346 03/19/03 05:53 PM
Joined: Jan 2003
Posts: 33
C
Member
Per 2002 NEC 358.26 : No more than 360 deg of bends between pull points.

Rich

#84347 03/19/03 05:53 PM
Joined: Jan 2003
Posts: 73
C
Member
Yes, if the offset's do not equal more than 90 degrees.

#84348 03/19/03 06:35 PM
Joined: Mar 2003
Posts: 92
G
gserve Offline OP
Member
Would you consider 2 regular box offsets more than 1 quarter bend?(90 degress)?

#84349 03/19/03 06:46 PM
Joined: Feb 2003
Posts: 138
W
Member
No.

They are typically 10 degrees each for a total of 20. Hence, 90+90+90+20+20=310 total degrees.

[This message has been edited by WebSparky (edited 03-19-2003).]


Dave
#84350 03/19/03 07:11 PM
Joined: Oct 2000
Posts: 5,392
S
Member
ok, i'll play..

i've thrown plenty of pvc in dithes that will assume the natural bend of the ditch.

is this 'bent'?

#84351 03/19/03 07:27 PM
Joined: Apr 2001
Posts: 507
G
Member
"is this 'bent'?"
Only if the AHJ can see it!

I once had a AHJ do a rough-in inspection. He counted every box offset as a 90° bend. He was the Senior Inspector for the State on Nebraska. He wouldn't listen to reason and it wasn't worth the trouble to go over his head.

Ever since that time I no longer use box offsets on conduit that will get covered with sheetrock.

GJ

#84352 03/19/03 07:55 PM
Joined: Apr 2001
Posts: 449
F
Member
When ever I offset EMT I use 30º bends because it's easy to do the math when the multiplier is 2. That would make my offsets 60º so one of them and 3 90º would still be okay. Your offset would have to use 2 bends greater than 45º to make it a violation and that would be a funky looking offset!

#84353 03/23/03 06:24 PM
Joined: Oct 2002
Posts: 210
S
Member
To me the bends in the ditch is more than just being about passing inspection. To me its a bend because its gonna cause that much more resistance come wire pulling time.

#84354 03/26/03 11:43 PM
Joined: Dec 2001
Posts: 440
Likes: 3
Member
You know it's a tough day when an AHJ counts box offsets, and considers "the bend of the ditch" part of the 360 degrees. So I think I would ask him, "If I'm bent over 90 degrees at the waist, does that count also?"


Singing Moon River,
Doc


The Watt Doctor
Altura Cogen
Channelview, TX