ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat
Recent Posts
Do we need grounding?
by gfretwell - 04/06/24 08:32 PM
UL 508A SPACING
by tortuga - 03/30/24 07:39 PM
Increasing demand factors in residential
by tortuga - 03/28/24 05:57 PM
Portable generator question
by Steve Miller - 03/19/24 08:50 PM
240V only in a home and NEC?
by dsk - 03/19/24 06:33 AM
New in the Gallery:
This is a new one
This is a new one
by timmp, September 24
Few pics I found
Few pics I found
by timmp, August 15
Who's Online Now
0 members (), 96 guests, and 10 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
#84135 03/11/03 06:01 PM
Joined: Mar 2003
Posts: 92
G
gserve Offline OP
Member
When is a main breaker required in a sub panel in a residential detached garage? Aso what is the min. feeder ampacity for 3 circuits?

Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

#84136 03/11/03 09:11 PM
Joined: Dec 2001
Posts: 440
Likes: 3
Member
gserve,
Consider the following:
408.16 Overcurrent Protection.
(A) Lighting and Appliance Branch-Circuit Panelboard Individually Protected.
Each lighting and appliance branch-circuit panelboard shall be individually protected on the supply side by not more than two main circuit breakers or two sets of fuses having a combined rating not greater than that of the panelboard.
Exception No. 1: Individual protection for a lighting and appliance panelboard shall not be required if the panelboard feeder has overcurrent protection not greater than the rating of the panelboard.
I'm sure the exception will work for you. As far as the ampacity of the feeder is concerned, I can't tell you anything without knowing the rating of the branch circuits.
Hope it helps,
Doc


The Watt Doctor
Altura Cogen
Channelview, TX
#84137 03/11/03 09:27 PM
Joined: Nov 2000
Posts: 2,148
R
Member
Don't forget that 225.31 requires a disconnect at the detached garage. 225.33 permits up to 6 breakers to serve as the required disconnect. 225.39(D) requires that the feeder disconnecting means have a rating of not less than 60 amps for this application. Note that the section does not actually require a 60 amps feeder, but only a 60 amp disconnecting means. I think that the intent was to require a 60 amp feeder circuit, but the code words don't actually say that.
Don


Don(resqcapt19)
#84138 03/11/03 09:37 PM
Joined: Feb 2003
Posts: 138
W
Member
Don't forget the grounding electrode!

And GFCI's!


Dave
#84139 03/11/03 09:49 PM
Joined: Mar 2003
Posts: 92
G
gserve Offline OP
Member
The branch circuits are 1 15A lighting 1 20A receptacle and 1 20A 240V air compresser

#84140 03/11/03 09:56 PM
Joined: Mar 2003
Posts: 92
G
gserve Offline OP
Member
Speaking of the elctrodes can I use the main service electrodes which are about 15' away from the garage without driving additional electrodes for the garage GES?

#84141 03/12/03 11:25 PM
Joined: Dec 2001
Posts: 440
Likes: 3
Member
I can dig it Don. So, gserve, you could set a small load center with 6 breaker spaces or less (if they make one less than 6 spaces), and not need to have a disconnect. If you want to add a panel of any greater size (in terms of breaker space), as Don pointed out, you're going to have to add a main, which can serve as a disconnect, or add a disconnect.
Regards,
Doc


The Watt Doctor
Altura Cogen
Channelview, TX
#84142 03/12/03 11:52 PM
Joined: Nov 2000
Posts: 2,148
R
Member
Doc,
The six disconnect rule is not based on the number of spaces in the panel, but the number of breakers installed. Just because it is possible to install more breakers in the future, doesn't make it a violation today.
Don


Don(resqcapt19)
#84143 03/13/03 08:59 PM
Joined: Dec 2001
Posts: 440
Likes: 3
Member
I'm with you Don. The reason I mentioned it, is because a friend of mine ran into this problem. He had some AHJ hammer him for it. The AHJ's was trying to prevent additional disconnects from being added in the future. My response was....How does he know that you won't add 2 pole breakers for other equipment, and therefore need a 12 space panel? (it was a single phase application) My buddy replied, "Who know's?"
So, let me retract my earlier statement, and say, "Based on some prior experience that a friend of mine had, be prepared, gserve, for the possibility that an AHJ, may walk onto your project, and want assurance that you, or someone in the future will not add breakers in that MLO panel, which would be a violation." So, gserve, it might be a good idea to give them a call, and see what kind of response you get from them.

Trying to be helpful,
Doc


The Watt Doctor
Altura Cogen
Channelview, TX

Link Copied to Clipboard
Powered by UBB.threads™ PHP Forum Software 7.7.5