#84105 03/10/03 02:54 PM
Can someone please give some advise on this.Running wiring through holes in a web beam floor joist.I don`t have them packed but I have 4- 14/2 cables in some and 12/2 and 10/3 in others and ahj says I`m bundling must derate.I thought they had to be tied or taped. Thanks
#84106 03/10/03 05:00 PM
'bundeling' is somewhat ill-defined, 310.15(b)(2)ex 5 can be used if your running MC or AC.
Table 310.15(b)(2)(a) w/310.16's ability to start @ the 90 deg collum should grant you some leverage
#84107 03/10/03 06:03 PM
Tom Offline
If all you have is four 2 wire cables, there is no problem. You will be derating to 70% of the 90 degree column.
The trouble starts when you hit the fifth 2 wire cable in the bundle which requires a 50% derating.
As for the 3 wire cables, if this is a single phase system, the neutral is not considered a current carrying conductor and if this is a 3 way switch cable, only 2 wires are current carrying.
#84108 03/10/03 07:46 PM
Only if the joist holes are longer than 2' does the derating apply.
It is between you and your inspector as to what you will agree on.