#84088 03/09/03 05:57 PM
Joined: Aug 2002
Posts: 141
E
elecbob Offline OP
Member
I did some load calcs for a residential triplex. Each unit totalled 50 amps. The house load was 55 amps. The service load totalled 174 amps. The building is in an undergrounded area and the only service voltage available is 480 volts, single phase. I want to install:
A 100 amp 480 volt safety switch.
A 50 KVA transformer to supply the 120/240 volts.
A meter pack rated at 200 amps.
4 - 60 amp panels.
Think it will fly?
Thanks Bob

Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

#84089 03/09/03 08:34 PM
Joined: Apr 2002
Posts: 558
C
Member
Bob, Are you saying that the utility will not supply you with a 120/240 volt service?

The only way I can imagine a utility accepting an installation as you described is to install a 480 volt meter before the disconnect and transformer then have 4 customer read meters on the secondary side of the transformer. How would the utility control future un-metered loads being connected to the disconnect or transformer?

Curt


Curt Swartz
#84090 03/09/03 11:15 PM
Joined: Aug 2002
Posts: 141
E
elecbob Offline OP
Member
I erred on this one. The utility wants to install a pad mounted transformer on a 48" by 56" pad in the back yard. Not good. My option is to install a meter ahead of my own transformer in the basement. I couldn't seperately meter the units but the heat and hot water are central so it shouldn't be a big deal. Not the best solution but cheaper and more doable.
bob
[This message has been edited by elecbob (edited 03-09-2003).]

[This message has been edited by elecbob (edited 03-10-2003).]