ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat
Recent Posts
Safety at heights?
by gfretwell - 04/23/24 03:03 PM
Old low volt E10 sockets - supplier or alternative
by gfretwell - 04/21/24 11:20 AM
Do we need grounding?
by gfretwell - 04/06/24 08:32 PM
UL 508A SPACING
by tortuga - 03/30/24 07:39 PM
Increasing demand factors in residential
by tortuga - 03/28/24 05:57 PM
New in the Gallery:
This is a new one
This is a new one
by timmp, September 24
Few pics I found
Few pics I found
by timmp, August 15
Who's Online Now
1 members (Scott35), 555 guests, and 34 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
#84013 02/27/03 12:10 PM
Joined: Nov 2000
Posts: 246
R
rmiell Offline OP
Member
I would like some comments on the following, concerning “bubble” wp covers.

Locations:
#1: 20a, 125v, outlet located outdoors, on the outside of a building.
A: Outlet will be “attended”
B: Outlet will be “un-attended”
#2: 20a, 125v, outlet located in a wash-down area, inside of a building.
A: Outlet will be “attended”
B: Outlet will be “un-attended”
#3: 30a, 250v outlet located outdoors, on the outside of a building.
A: Outlet will be “attended”
B: Outlet will be “un-attended”
#4: 30a, 250v outlet located in a wash-down area, inside of a building.
A: Outlet will be “attended”
B: Outlet will be “un-attended”

Note: All locations are considered wet locations by code.

Questions:
On which installation is a bubble type cover required? By which article?
On which installation is a regular flat type wp cover allowed? By which article?

Thanks, Rick Miell

Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

#84014 02/27/03 12:25 PM
Joined: Nov 2000
Posts: 2,148
R
Member
Rick,
1(A) and (B) and 3(A) and (B) require bubble covers per 406.8(B)(1).
All of the others require a bubble cover for un-attended use and standard wetherproof cover for attended use per 406.(B)(2).
Don

My answer is not correct. I read the amps for item #3 as 20 when I posted the original answer. Item 3 also falls under 406.8(B)(2) and the type of cover is dependent upon the usage.
don

[This message has been edited by resqcapt19 (edited 03-03-2003).]


Don(resqcapt19)
#84015 02/27/03 05:14 PM
Joined: Jan 2002
Posts: 163
D
Member
rmiell - the verbage you are using "attended, unattended" is used in the 1999 NEC (410-57) to determine whether the 'bubble' is to be used. In the 2002 NEC this verbage is eliminated (and this section is moved to a new article (406) and the code now requires the 'bubble' in all outdoor wet locations.

#84016 02/27/03 05:40 PM
Joined: Nov 2000
Posts: 2,148
R
Member
Dana,
That is not exactly what 406.8(B) says. If the receptacle is rated 15 or 20 amp and 125 or 250 volts and is outside in a wet location it will require a bubble cover. If it has any other rating and is outside in a wet location, the type of cover is base on "attended" or " not attended" usage.
don


Don(resqcapt19)
#84017 02/27/03 08:19 PM
Joined: Oct 2000
Posts: 5,392
S
Member
bit of a threadjack /]

Is there a decent 'bubble' cover on the market? all the plastic ones i've used and/or seen don't last long


[Linked Image]

#84018 02/27/03 08:38 PM
Joined: Dec 2002
Posts: 110
W
Member
..But...
406.8(B)(2) apply to receptacles other than those described in (B)(1) and covers indoor and outdoor wet locations.
.ie, 406.8(B)(2)b A receptacle installed in a wet location where the product intended to be plugged into it will be attended while in use(e.g., Portable tools and so forth) shall have an enclosure that is weatherproof when the attachment plug is REMOVED.

That one is listed as a new change.