0 members (), 376 guests, and 7 robots.
#83652 02/11/03 04:00 PM
EVAD7 Offline OP
Does a system need to be extended throughout the entire building? for example, three phase 4w 240 Volt, Feeder just for 3 phase load, Do you carry the neutral even if it isn't used?
#83653 02/11/03 04:36 PM
It depends on how forward-thinking you want to be. You didn't give enough information for a better answer. It's cheaper to install a little extra now, than re-do the work later. What if you need to install some control circuits?
#83654 02/11/03 04:44 PM
EVAD7 Offline OP
This is a code question,is there any requirement to extend the system in each feeder?
#83655 02/11/03 06:09 PM
There is no requirement to install a neutral in a feeder or branch circuit that does not utilize it.
#83656 02/11/03 07:06 PM
EVAD7,
What you're saying rings a bell, but I can't find it.
#83657 02/11/03 08:29 PM
Ron Offline
The neutral needs to be brought to the main disconnect if it is a 3 phase 4 wire service.
Ron
