I am refering to the 1996 NEC Handbook, on page 255 article 318-11 the book has a diagram 318-3 shows a one cable distance between each cable. I cannot find a code reference that says you shall maintain one cable width between each cable. What I have is MC cable with 4 5ookcmil conductors. Is there a mandatory spacing requirement, and if so what is the code reference. Thanks Joe
Stay up to Code with the Latest NEC:
>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides
Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep
>> 2020 NEC & Related Reference & Study Guides
#83424 01/30/03 05:55 PM
I dont have my 96 with me but in the 99NEC 318-11 the spacing is allowed for ampacity reasons(derating)
[This message has been edited by txsparky (edited 01-30-2003).]
Donnie
#83425 01/30/03 06:05 PM
The spacing configuration you refer to permits ampacities in accordance with Table B.103.3 in Annex B of the '02 code.
Otherwise, 392.9 refers to tray fill based on cable sizes.
[This message has been edited by Redsy (edited 01-30-2003).]
#83426 01/31/03 10:27 AM
JBD Offline