ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat
Recent Posts
UL 508A SPACING
by ale348 - 03/29/24 01:09 AM
Increasing demand factors in residential
by tortuga - 03/28/24 05:57 PM
Portable generator question
by Steve Miller - 03/19/24 08:50 PM
Do we need grounding?
by NORCAL - 03/19/24 05:11 PM
240V only in a home and NEC?
by dsk - 03/19/24 06:33 AM
New in the Gallery:
This is a new one
This is a new one
by timmp, September 24
Few pics I found
Few pics I found
by timmp, August 15
Who's Online Now
1 members (ale348), 302 guests, and 14 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
Page 1 of 2 1 2
#83129 01/14/03 01:22 AM
Joined: Aug 2002
Posts: 141
E
elecbob Offline OP
Member
Is there an NEC requirement that conductors, such as those from the circuit breaker panel to the cold water pipe, be insulated if they are ran through metal raceways such as EMT or metal wiremold?
Thanks in advance.
Bob

Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

Joined: Apr 2002
Posts: 197
G
Gwz Offline
Member
It appears you are referring to the Grounding Electrode Conductor (GEC) which must be installed as per 250.64(E) {conductor bonded to each end of the metal raceway enclosing the GEC}.

To answer the question of insulated conductor, the answer would be " NO" for copper GEC and maybe for Aluminum GEC. See 250.64(A).

Joined: Mar 2001
Posts: 2,056
R
Member
250.118(1) permits an uninsulated EGC.

Joined: Apr 2002
Posts: 197
G
Gwz Offline
Member
When he said ' cold water pipe ' I am assuming GEC.

Aluminum Conductor in/near earth has restrictions.

Joined: Dec 2002
Posts: 32
W
Junior Member
Its my understanding that if you run the grounding electrode in a metal pipe then it has to be bonded to the metal pipe. Something about setting up electromagnetic waves or something. If we do it we use a pipe nail or a clamp to make it continuous with the pipe its in although if it was bare it would seem like it would naturally be in contact. Thats why we usually run it in pvc. I hope i understood what you were getting at.

Joined: Apr 2002
Posts: 197
G
Gwz Offline
Member
What is a ' pipe nail ' that would bond the GEC to each end of a metal raceway ?

Note, a metal raceway enclosing a GEC could be a metal - wireway, junction box, trough, wiremold, etc.

The GEC must be bonded to both ends of a metal enclosure - 250.64(E).

Joined: Mar 2001
Posts: 2,056
R
Member
Sorry about the mix-up. (EGC v. GEC)
I should have read more caerefully

Joined: Oct 2002
Posts: 5
M
Junior Member
Gwz
it seems to me that 250.64e says you have to bond each end of a metal raceway if it is not electrically continous. if you used one peice of emt to enclose a gec wouldnt that be electrically countinous?

Joined: Apr 2002
Posts: 197
G
Gwz Offline
Member
When an GEC is inclosed in a metal raceway, standard locknuts, etc. are not considered 'continuous' unless items are bonded together.

See examples in figures 7-13 and 7-14 of the 8th Edition of the Soares Book on Grounding.

In figure 7-14, I believe, a 'setscrew locknut' would serve the purpose of the bonding bushing in the panelboard/conduit connection and also for the conduit to enclosures of figure 7-13.

Joined: Feb 2002
Posts: 2,233
H
Member
Isn't there something in the code about concentric knockouts? They have to be rated for the voltage? I believe it has to do with 480 volts etc. My code book is in the office.

Harold

Page 1 of 2 1 2

Link Copied to Clipboard
Powered by UBB.threads™ PHP Forum Software 7.7.5