I posted this at the M.H. forum also.
Talking to another electrician today who works in another area.
He tells me there is an inspector in this area, who says, when using NM in a commercial building, the NM in attics and basements must be enclosed on both sides, within 15 minute finish rating in living area and attic or basement area.
He said the inspector is using (twisting in my oppinion) the wording of 334.10(3).
I proceeded to tell him I was glad we do zilch in NM work and don't work in this area.
After thinking about it,I thought I would see what oppinions would come up here.
Roger
|
|
|
|
Joined: Oct 2002
Posts: 210
Member
|
I have never run into this before, but he may have a point after reading 334.10(3). Learn something new everyday. I almost always use MC cable anyway for commercial.
|
|
|
|
Joined: Oct 2000
Posts: 5,392
Member
|
requiring all residential basements to have a 15 min. fire rating would be a stretch...but what trade would he come down on?
|
|
|
|
Joined: Nov 2000
Posts: 246
Member
|
Why on both sides? Doesn't 1/2" sheetrock provide a 15 minute rating? Or is it 3/4"? Either way, if this rated material meets the requirement of a 15 minute barrier, anything on the other side has no effect.
Rick Miell
|
|
|
|
Joined: Apr 2002
Posts: 7,381 Likes: 7
Member
|
Clue me in guys: Quote from above: "He tells me there is an inspector in this area, who says, when using NM in a commercial building, the NM in attics and basements must be enclosed on both sides, within 15 minute finish rating in living area and attic or basement area."
Are we saying above that the ceilings must be 15 min. fire rated: and the "floors have to be 15 min fire rated also??
Or to put it another way: OPen joist ceilings, or attic floors CANNOT have NMC wiring???
1/2" sheetrock is at least a 15 min fire rating. 2 layers of 5/8" make a 1 hour wall I believe. Tommorow, I have to ask the Building Inspector, and the Electric Sub-Code Official (Head Inspector) for clarifications.
John
John
|
|
|
|
Joined: Oct 2000
Posts: 5,392
Member
|
well good luck John, somehow insinuating mc cable for residential wiring reeks of that steel tube institute's vengance on the 3 strory nm deal....
|
|
|
|
Joined: Apr 2002
Posts: 7,381 Likes: 7
Member
|
The clarifications will have to wait until Tuesday evening, as both gentlemen where "out" today, & I don't go back 'till Tuesday John
John
|
|
|
|
Joined: May 2002
Posts: 1,716
OP
Member
|
I hate it when somebody or an inspector uses (in their oppinion) the " thats not the intent" clause. But in this case, the pure wording of 334.10{3}, IMO, is not the intent. Roger
|
|
|
|
Joined: Feb 2002
Posts: 2,233
Member
|
I am reading the IAEI "Analysis of the 2002 NEC" book and on page 185 in reference to 334.10 it says "Type NM, Type NMC and Type NMS cables shall be permitted to be used in the following:
(1) One- and Two-family dwellings.
(2) Multifamily dwellings permitted to be of Types III, IV, and V construction except as prohibited in 334.12
(3) Other structures permitted to be of Types III, IV, and Type V construction except as prohibitied in 334.12. Cables shall be concealed within walls, floors or ceilings that provide a thermal barrier of material that has at least a 15-minute rating as identified in listings of fire-rated assemblies."
Does this help?
|
|
|
|
Joined: Oct 2000
Posts: 5,392
Member
|
a 15 min f-rating to protect the dwelling or the dwellings occupants??
|
|
|