The 1999 NEC 230.30(a)(4) text, which I believe would have covered the Xo being grounded and not a conductor extended to the system disconnect, by noting on a violation " 1999 NEC 250.24(b)", but the 2002 NEC did not retain those words.
Also have not seen the existing 4160V source for this Plant. Believe plant is about 25 years old.
At present time, do not know if the 4160V is delta or wye.
If a delta 4160V system, is an EGC required (in same raceway) with each feeder along with the individual 5KV drain ( sheild ) of each Phase cable? Appears 250.4(B)would require all equipment to be so bonded.
As can be seen by the questions, have not had many HV in plant systems.