#82564 11/27/02 10:52 AM
Joined: Oct 2002
Posts: 4
B
BIGDOGG Offline OP
Junior Member
can't find in nec , service entrance conductors shall be no longer than 6 ft ,in basement ,before entering service equipment

Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

#82565 11/27/02 11:19 AM
Joined: Nov 2000
Posts: 2,148
R
Member
You won't find that because the code does not specify a maximum length of service conductors within a building. Look at 230.70(A)(1).
Don


Don(resqcapt19)
#82566 11/27/02 11:55 AM
Joined: Sep 2002
Posts: 2
V
Junior Member
I think that is a local law .The ahj in your area has probably adopted the"six-foot" ruleas a means to set the standard.The nec says that the main ocpd should be as "close as possible to the meter."you may find that in certain applications the inspector may allow a length longer than six feet.

#82567 11/27/02 02:32 PM
Joined: Oct 2002
Posts: 4
B
BIGDOGG Offline OP
Junior Member
THANKS FOR THE QUICK ANSWER ,HAVE A SAFE AND HAPPY HOLIDAY .

#82568 11/30/02 09:45 AM
Joined: Jun 2002
Posts: 186
M
mj Offline
Member
the purpose for the ahj to have a limit for se conductors is "overcurrent protection" we have a five ft rule in my area. if no rule was in place some electricians would have a hundred feet or more of un-protected se condutors without any type ocpd see section #230.70 2002 nec, also see sec #230.6, conductors considered outside the building.