ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat
Recent Posts
Safety at heights?
by gfretwell - 04/23/24 03:03 PM
Old low volt E10 sockets - supplier or alternative
by gfretwell - 04/21/24 11:20 AM
Do we need grounding?
by gfretwell - 04/06/24 08:32 PM
UL 508A SPACING
by tortuga - 03/30/24 07:39 PM
Increasing demand factors in residential
by tortuga - 03/28/24 05:57 PM
New in the Gallery:
This is a new one
This is a new one
by timmp, September 24
Few pics I found
Few pics I found
by timmp, August 15
Who's Online Now
1 members (Scott35), 519 guests, and 18 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
#82396 11/08/02 03:46 PM
Joined: Jun 2001
Posts: 21
V
VOLTS Offline OP
Member
I need to install A new air compressor in an area that has the power maxed out. Can I feed off of A 600amp sub station breaker to a 200amp fused disconnect what will my conductors be rated at 600 or 200 the distance is about 40 feet.

Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

#82397 11/08/02 05:07 PM
Joined: May 2001
Posts: 176
W
Member
If your substation breaker is presently a spare, then the conductors need to be good for 600A, paralell 350KcMil will do the job. Now terminating them in a 200A disconnect might be a problem. But you could tap the 350's with 3/0 for terminations. Check Art. 240-21 for the appropriate application to your situation.
Hope this helps.

#82398 11/09/02 10:34 AM
Joined: Mar 2002
Posts: 582
R
Ron Offline
Member
Especialy if there is already a lack of distribution, then install a 600A panelboard/switchboard, and take a 200A breaker from there. Next project, you'll be sorry you wasted a big breaker for a small load.


Ron
#82399 11/11/02 08:48 AM
Joined: Jun 2001
Posts: 21
V
VOLTS Offline OP
Member
Thank you for the ideas. I have A hard time convincing the boss that we need to think about the future. He only worries about how much this project costs not the problems it will cause for others down the road. thanks again