#82299 11/01/02 07:33 PM
Joined: Nov 2002
Posts: 14
S
Member
I would like to hardwire a 250W/120V transformer for Low Voltage undercabinet lighting to the microwave outlet, which is 220V/30A. Is this permissible?
Although the oven specs require 30A/220V, the oven only uses 950W (doesn't sound right, but there it is in B&W at www.geappliances/advantium/models). So ampacity should not be a problem.

Second option: Can I install a 120V recepticle instead of hardwiring the transformer, using #10 wire for the tap? Can I use #10 wire with a standard 120V 15A recepticle?

Steve.

Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

#82300 11/01/02 10:11 PM
Joined: Apr 2002
Posts: 558
C
Member
Steve - I don't have a spec. sheet in front of me on this oven but the 950 watt's is probably the output of the microwave it is not the input. The reason this unit requires such a large circuit is for the halogen lights it uses for cooking in addition to the microwave function.

You should not connect any lights to this circuit. You need to connect your lighting to a 15 or 20 amp general lighting circuit.


Curt Swartz