Joined: Oct 2002
Posts: 210
S
spyder Offline OP
Member
I know many manufacturers require GFCI protection for fixtures when used in Tub and Shower locations.

Does the NEC also have this requirement?

Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

Joined: Apr 2002
Posts: 558
C
Member
The NEC does not require GFCI protection of fixtures over tub or shower enclosures but if the fixture manufacture requires protection then you must provide it.

You say that many manufactures require GFCI protection? I have never seen this requirement on any fixtures other than fans.

Curt


Curt Swartz
Joined: Oct 2002
Posts: 210
S
spyder Offline OP
Member
Curt,

Your right, now that I think about it, I have only seen it required by manufactures of bath fan and bath fan/lite combos.

Joined: Nov 2000
Posts: 2,236
Likes: 1
Member
If I'm not mistaken, Progress Recessed Canisters (P87-AT) and the Shower Trims (P8025-60) require GFCI protection for use in shower stalls.


-Virgil
Residential/Commercial Inspector
5 Star Inspections
Member IAEI
Joined: Oct 2000
Posts: 5,392
S
Member
Q~ how many take advantage of the EX to 210.11(C)(3) here vs. blank faced GFI's?

Joined: Oct 2002
Posts: 210
S
spyder Offline OP
Member
Sparky,

I almost always provide GFCI protection in tub and shower enclosures for fixtures regardless of whether or not the manufacturer requires it. I do so most often using the execption you mention.

Joined: Oct 2000
Posts: 5,392
S
Member
spyder,
me too.
those blank faced GFI's were a hard sell for me.
[Linked Image]