While installing circuits in a ceiling of a commerical building I was told I have to remove all the abandon wiring in the ceiling. There is a lot of old wire. Is there any NEC code that requires this? Boomer
#81833 09/22/02 11:49 PM
Unless they are tagged for future use, I believe they do have to come down.there are NEC regulations concerning abandoned wire.
[This message has been edited by Sean WB (edited 09-22-2002).]
I did not get as think so badly as you shocked I did.
#81834 09/23/02 06:43 AM
I thought just Fire Alarms required tags....
#81835 09/23/02 07:05 AM
Is this a building renovation or are you just adding a few circuits?
#81836 09/23/02 08:49 AM
The "remove or tag" rule only appears in Chapter 7 and 8 Articles. At this time there is no rule to "remove or tag" Chapter 3 wiring. It is a good practice to remove the
abandoned wiring, and is often required by the job specs.
Don