Joined: Sep 2002
Posts: 2
M
mikeb Offline OP
Junior Member
Can anybody tell me why a convenience outlet is required for an above ground pool? It doesn't make any sense to me.


MikeB
Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

Joined: Jan 2001
Posts: 1,044
Tom Offline
Member
Welcome to the forum.

The requirement for the receptacle is there so that when Henry Homeowner wants to plug in some utilization equipment near the pool he will have access to a properly installed GFI protected receptacle & he won't need to run an extension cord to a receptacle further away that may not be GFI protected.

Tom


Few things are harder to put up with than the annoyance of a good example.
Joined: Nov 2000
Posts: 2,148
R
Member
Mike,
The code making panel assumes that portable electric devices like radios, stereos, ect. will be used in the pool area. By requiring a GFCI protected receptacle close by, it is likely that this GFCI protected receptacle would be used to power any devices used near the pool. If this receptacle was not required, then cords would be run from other outlets that may not be GFCI protected.
Don


Don(resqcapt19)
Joined: Sep 2002
Posts: 2
M
mikeb Offline OP
Junior Member
Thanks for the responses and they make sense. However, I built my house 5 years ago and I have a GFI outlet located on my house which happens to be 22 feet away from the waters edge. I spoke to my code official yesterday and he says that whoever inspects it might allow it if he's in a good mood. If not, I guess I'll fail and have to run another outlet. I think the codes need a little updating. Thanks again for responding.


MikeB
Joined: Nov 2000
Posts: 2,148
R
Member
Mike,
Why does it need updating? You have to draw the line somewhere.
Don


Don(resqcapt19)
Joined: Jan 2001
Posts: 1,044
Tom Offline
Member
Mike,

If you feel strongly about this issue, you should submit a proposal to change the NEC. After all, it is our code and is open for input from any source. Forms for submitting a proposal can be found in the back of your codebook.

Good luck.

Tom


Few things are harder to put up with than the annoyance of a good example.
Joined: Feb 2002
Posts: 2,233
H
Member
If I were inspecting this job and the receptacle is 22 feet away, and in good shape, and on somethig solid (like a house) I would pass this job. I had a job like this several years ago. The inspector say an outlet solidly attached to a house but it was 21 feet away from the new hot tub in the back yard. So he made me move the outlet off the house, down under a side walk, more into the middle of the yard,(where it can get hit by a lawnmower, or people can trip over it.)on a rocket post so that the new receptacle was 19-18 feet away from the spa. Is this logical? I don't think so.