ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat
Recent Posts
Do we need grounding?
by gfretwell - 04/06/24 08:32 PM
UL 508A SPACING
by tortuga - 03/30/24 07:39 PM
Increasing demand factors in residential
by tortuga - 03/28/24 05:57 PM
Portable generator question
by Steve Miller - 03/19/24 08:50 PM
240V only in a home and NEC?
by dsk - 03/19/24 06:33 AM
New in the Gallery:
This is a new one
This is a new one
by timmp, September 24
Few pics I found
Few pics I found
by timmp, August 15
Who's Online Now
0 members (), 205 guests, and 28 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
#81382 08/05/02 11:58 AM
Joined: Aug 2002
Posts: 3
A
Junior Member
Can i run 2 2" condduits up from my panel through the double plate to run the wiring for my house?Contractor says it will weaken my wall but its a inside wall not load bearing.Also are there any violations here or things to look for?Found the site through a electrician freind of mine.This is great maybe I wont have to bug the guys at the supply house now.

Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

#81383 08/05/02 12:45 PM
Joined: May 2002
Posts: 132
E
Member
I wouldn't think twice about not running the conduits. Just seperate the conduits a little and be sure to protect against screws or nails. Plumbers don't bat an eye running vent pipes?

#81384 08/05/02 12:54 PM
Joined: May 2002
Posts: 1,716
R
Member
Not that I agree, but if these conduits are over 24" your inspector might bust you on bundling. [Linked Image]

Roger

#81385 08/05/02 02:22 PM
Joined: Oct 2000
Posts: 2,749
Member
Check 2002 NEC, 312.5(C) Cables. Where cable is used, each cable shall be secured to the cabinet, cutout box, or meter socket enclosure.

Exception: Cables with entirely nonmetallic sheaths shall be permitted to enter the top of a surface-mounted enclosure through one or more nonflexible raceways not less than 450 mm (18 in.) or more than 3.0 m (10 ft) in length, provided all the following conditions are met:

(a) Each cable is fastened within 300 mm (12 in.), measured along the sheath, of the outer end of the raceway.

(b) The raceway extends directly above the enclosure and does not penetrate a structural ceiling.

(c) A fitting is provided on each end of the raceway to protect the cable(s) from abrasion and the fittings remain accessible after installation.

(d) The raceway is sealed or plugged at the outer end using approved means so as to prevent access to the enclosure through the raceway.

(e) The cable sheath is continuous through the raceway and extends into the enclosure beyond the fitting not less than 6 mm (1/4 in.).

(f) The raceway is fastened at its outer end and at other points in accordance with the applicable article.

(g) Where installed as conduit or tubing, the allowable cable fill does not exceed that permitted for complete conduit or tubing systems by Table 1 of Chapter 9 of this Code and all applicable notes thereto.


FPN:See Table 1 in Chapter 9, including Note 9, for allowable cable fill in circular raceways.

See 310.15(B)(2)(a) for required ampacity reductions for multiple cables installed in a common raceway.


Joe Tedesco, NEC Consultant
#81386 09/17/02 11:36 PM
Joined: Apr 2001
Posts: 518
J
Member
UBC allows 60% (I think) hole in non-bearing members. A 2x4 plate is only wide enough for 1 1/2" pipe. I don't care what plumbers do...


Link Copied to Clipboard
Powered by UBB.threads™ PHP Forum Software 7.7.5