ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat
Recent Posts
Safety at heights?
by gfretwell - 04/23/24 03:03 PM
Old low volt E10 sockets - supplier or alternative
by gfretwell - 04/21/24 11:20 AM
Do we need grounding?
by gfretwell - 04/06/24 08:32 PM
UL 508A SPACING
by tortuga - 03/30/24 07:39 PM
Increasing demand factors in residential
by tortuga - 03/28/24 05:57 PM
New in the Gallery:
This is a new one
This is a new one
by timmp, September 24
Few pics I found
Few pics I found
by timmp, August 15
Who's Online Now
1 members (Scott35), 540 guests, and 32 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
Page 2 of 2 1 2
Joined: Nov 2000
Posts: 2,148
R
Member
Using the information from the Bussmann point-to-point short circuit calculations I come up with the following. I assumed a 1000 amps available at the breaker, 120 volt single phase circuit, and 100' of wire to the fault. The fault currents at 100' are:
#12 270amps, #10 370 amps, #8 425amps, #6 538amps, and #4 647amps.
Don(resqcapt19)


Don(resqcapt19)
A
Anonymous
Unregistered
http://www.bussmann.com/tech/S_circuit.html

Quote
I assumed a 1000 amps available at the breaker, 120 volt single phase circuit, and 100' of wire to the fault.
I had suggested 20' for the reason that the longer runs do act significantly to reduce the SCA.

Quote
The fault currents at 100' are:
#12 270amps, #10 370 amps, #8 425amps, #6 538amps, and #4 647amps.
I am not sure that this is the sole criterion.

I want to know in the case of a 20 A CB how many joules could be delivered before the breaker opens. My intuition tells me that the CB will open sooner with the higher fault current.

I mean let's suppose that the SCA was 30 A because the run was 2000'. I would not consider this safer.