1 members (Scott35), 216 guests, and 11 robots.
#80866 06/09/02 01:31 PM
Eandrew Offline OP
If a conductor is for a continuous load and feeds the load through a raceway of more than three conductor, do you only apply the fill correction and forget the continuous load aspect. Or do you take them both into consideration?
#80867 06/11/02 03:54 PM
Bob Offline
You must use the derating for continous
load and conduit fill when derating these conductors.
#80868 06/11/02 05:29 PM
Eandrew Offline OP
Thanks Bob.