ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat
Recent Posts
Safety at heights?
by gfretwell - 04/23/24 03:03 PM
Old low volt E10 sockets - supplier or alternative
by gfretwell - 04/21/24 11:20 AM
Do we need grounding?
by gfretwell - 04/06/24 08:32 PM
UL 508A SPACING
by tortuga - 03/30/24 07:39 PM
Increasing demand factors in residential
by tortuga - 03/28/24 05:57 PM
New in the Gallery:
This is a new one
This is a new one
by timmp, September 24
Few pics I found
Few pics I found
by timmp, August 15
Who's Online Now
1 members (Scott35), 235 guests, and 27 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
#80760 05/15/02 03:28 PM
Joined: Oct 2000
Posts: 2,749
Member
Question from:

Theodore P. Von Sydow
US. Department of State

My question in a nutshell: Can a conductor pass through a transformer if it is not connected to the transformer?

Can the transformer be used as a raceway for a circuit or conductor that is not directly related to the function of the transformer?

Thank you


Joe Tedesco, NEC Consultant
Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

Joined: Mar 2002
Posts: 582
R
Ron Offline
Member
If there is no violation of voltage class' of insulation, or type of wiring (communications, fire alarm, etc), seems ok.


Ron
Joined: Mar 2001
Posts: 2,056
R
Member
This is not a good practice.
If the transformer fails, you would have to remove the conductor and disrupt it's loads in order to replace the transformer.

Joined: Oct 2000
Posts: 2,749
Member
I agree, no foreign wires are to be passed through the transformer. I expect that there will be many who wear the AHJ hat that will agree. It is also common knowledge that all conductors are not to be passed through an area that originates in the top section -- the label in the transformer enclosure will cleary identify this and other restrictions.


Joe Tedesco, NEC Consultant
Joined: Mar 2002
Posts: 582
R
Ron Offline
Member
I also agree, not a good practice. I think the original questions infers that the poster wants to know if it is a code violation. I don't find a violation.


Ron

Link Copied to Clipboard
Powered by UBB.threads™ PHP Forum Software 7.7.5