Exactly what taps are being referred to in Table 210.14. that are allowed to tap #14 to a 20 amp ckt? Fixture taps?
The question came up about running a 20 amp ckt. for DW/GD and running 2 #14-2s to the loads.
I don't go for it.
Stay up to Code with the Latest NEC:
>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides
Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep
>> 2020 NEC & Related Reference & Study Guides
#80596 05/02/02 08:00 PM
Redsy,
where is this in the 02' [Linked Image]
#80597 05/02/02 09:42 PM
Redsy,
I think that you are referring to Table 210.24. The only applications that I know of are in the exception to 210.19(A)(4). It appears that if you hardwired the dishwasher and the garbage disposal, and the combined loads did not exceed 20 amps and the #14 tap conductors did not exceed 18", that the installation would be code compliant.
Don(resqcapt19)
Don(resqcapt19)
#80598 05/02/02 10:36 PM
Redsy Offline OP
Thanks, Don. I think I'd skip this attempt at saving about $.03.
sparky, Don was right, I meant table 210.24.