Used to be, I'd put bedroom and bathroom lights on a circuit, the receptacles in the bedroom on a circuit and the bath GFCI on a dedicated circuit. Now with AFCI's entering the picture, I've opted to have the bedroom lights on the end of the receptacle chain for cheaper AFCI protection, and now the vanity and vent-fan/light combos are all alone...
My question is:
It appears that 210.11(C)(3) Exception gives me the leeway to put said vanity and fan/light with the GFCI circuit... just to have 210.23(A) Exception take it back away from me...
Is this a code loop or am I just really tired tonight?
If this were a T&M job rather than one grossly underbid (again?!?), it would be moot...
Another question in same vein...
Let's assume I can't put the lights with the rest of the bath circuit. Two basins in the bathrooms pretty much dictate two receptacles. I'm allowed to combine them on a circuit, but with the 1875W hair dryers and the habit of some ladies to have the curling iron warming up as she blow dries the hair... well you get the picture...
If it were T&M, again I would give them two GFCI's dedicated.
[This message has been edited by sparky66wv (edited 03-27-2002).]
-Virgil Residential/Commercial Inspector 5 Star Inspections Member IAEI
|
|
|
|
Joined: Jan 2002
Posts: 1,457
Member
|
My understaniding is that you must wire a 20 amp circuit for the gfi which can also serve other loads within that bathroom only. Also if there are two sinks and the gfi is within 36 inches of both of them you really only need one.
|
|
|
|
Joined: Oct 2000
Posts: 4,116 Likes: 4
Member
|
Virgil, I don't think the Curling Iron is a problem. What is the wattage on those? I've only got 15A circuits and 5 Females around My House and have never tripped a Breaker. (No, not FPE ) Bill
Bill
|
|
|
|
Joined: Oct 2000
Posts: 5,392
Member
|
AFCI's have everyone changing and or challenging methods....a 'backburn'scenario I believe the 210.11 EX overrules 210.23 EX, we may get into a 'NEC style' interpetation though....as for ampacity 210.23 and the 50-80% rules appear.....(2)'s dual reference to lighting units is confusing here...... (1) Cord-and-Plug-Connected Equipment. The rating of any one cord-and-plug-connected utilization equipment shall not exceed 80 percent of the branch-circuit ampere rating. (2) Utilization Equipment Fastened in Place. The total rating of utilization equipment fastened in place, other than luminaires (lighting fixtures), shall not exceed 50 percent of the branch-circuit ampere rating where lighting units, cord-and-plug-connected utilization equipment not fastened in place, or both, are also supplied.
|
|
|
|
Joined: Oct 2000
Posts: 4,116 Likes: 4
Member
|
Virgil, I just looked at 2 items this morning. The Curling Iron was 38W and a Straightener was 170W. Not near enough to warrant another circuit. Sparky, (1) Cord-and-Plug-Connected Equipment. The rating of any one cord-and-plug-connected utilization equipment shall not exceed 80 percent of the branch-circuit ampere rating. If you can figure out how 1875W Hair Dryers get away without having a 20A plug please tell us. That one really gets me. Bill
Bill
|
|
|
|
Joined: Nov 2000
Posts: 2,236 Likes: 1
OP
Member
|
Thanks guys, a wealth of knowledge as always...
-Virgil Residential/Commercial Inspector 5 Star Inspections Member IAEI
|
|
|
|
Joined: Oct 2000
Posts: 5,392
Member
|
Bill, lobbyists.......
|
|
|
|
Joined: Dec 2000
Posts: 218
Member
|
Bill, I have the same problem. Just bid a beauty shop and they have 2 stations on a 20 A breaker with a 1850 hair dryer at each one and both used at the same time ocassionally. They must use a different way to figure amperage than P=IV.
|
|
|
|
Joined: Oct 2000
Posts: 5,392
Member
|
They must use a different way to figure amperage than P=IV. same as vacuum cleaners?........ 5 Females around My House come clean here Bill... when have you had the opportunity to view a hairdryer up close??? [This message has been edited by sparky (edited 03-29-2002).]
|
|
|
|
Joined: Jan 2002
Posts: 1,457
Member
|
Hey bill, what kind of curling iron do you use, and how is the hair staightener working out for you?
|
|
|
Posts: 57