Portable generator question
by Steve Miller - 03/19/24 08:50 PM
240V only in a home and NEC?
by dsk - 03/19/24 06:33 AM
2 members (sabrown, Scott35), 137 guests, and 7 robots.
#80249 03/22/02 03:36 PM
does a dish washer require a seperate circuit or not ?
Stay up to Code with the Latest NEC:
>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides
Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep
>> 2020 NEC & Related Reference & Study Guides
#80250 03/22/02 05:26 PM
Tom Offline
Well, it depends on how much of a load the dishwasher is. Start at 422-10(b) which refers to 210-23 if the circuit will supply the dishwasher and other loads.
If the dishwasher is cord & plug connected & is portable, it cannot exceed 80% of the circuit rating.
If the dishwasher is fastened in place, it cannot exceed 50% of the circuit rating if the circuit also supplies any of the other loads mentioned in 210-23(a).
Few things are harder to put up with than the annoyance of a good example.
#80251 03/22/02 05:40 PM
That is as long as it is not put on the small appliance circuit, ala
210.52(B)2 No other outlets. The two or more small appliance branch circuits specified in 210.52(B)1 shall have no other outlets.
So I would say yes it needs its own circuit.
-Mark-
#80252 03/22/02 08:54 PM
Different codes have different requirements.
From the 1998 ICC 1 & 2 Family dwelling Code, it is clear that the recept for the dishwasher may be on the small appliance circuits:
"Other receptical outlets provided ... shall be supplied by the small appliance branch circuits or other branch circuits."
I prefer to place the dishwasher, refrigerator, and disposal on one dedicated circuit. That might be an option for you.
#80253 03/22/02 09:31 PM
My preference is simply to overwire. This is NOT a bidwinner, only condusive to a good nights sleep...
All my kitchens have seperate appliance circuits
( which is why i need a 40 cir MLO {200A} panels in 100A calc'ed homes...)
WHY?
because the majority of old work problems is lack of ampacity....
#80254 03/23/02 11:22 PM
i think the frig dishwasher and disposal would be to much on one circuit.
i usually run one circuit to each
#80255 03/24/02 08:45 AM
eman
The refrigerator is allowed to be on the samll appliance branch circuit, or not your choice.
The Dishwasher and disposer are not allowed to be on the small appliance circuits.
They must be on their own circuits.
-Mark-
#80256 03/24/02 08:48 PM
A sepater ckt. for a GD seems overkill.
I like a 20 amp ckt. for GD & DW.
Dedicated 15 amp for frig.
#80257 03/24/02 08:49 PM
I'm more concerned with hte defrost cycle of the frig. than the running cycle. Anyone got the numbers?
#80258 03/24/02 09:29 PM
I'm in agreement with the majority.
I give dish/disp it's own cicuit. Frig. is always on its own. Micro/stove electronic ignition, on its own, too many inspectors have insisted on this one, micros are too big and bad nowadays.
Two small appliance as per code, yet I try not to exceed 3 outlets or 4 on each one.
And all of this depends on the homeowner with their specific appliances in mind, let's get toaster oven and a countertop micro going together, oh a little coffee, and some toast too, and they are all on the same wall.
Overwiring up front can avoid the service calls. Everything seems to get bigger and badder.
Everything is networked and typically numerous 1/2" HRS, 3/4" if the wire is dumped ASAP.