#80107 02/28/02 07:01 PM
Joined: Jan 2002
Posts: 1,457
E
Member
Bring the book and let him read it. If he can't seem to uderstand at that point maybe it's time to go over his head. County or state official perhaps. I have done this before trying not to be confrontational and it has worked out fine. If you know you are right and I beleive you are you must do the right thing. Who knows what else this guy is having people do. Just because he is an inspector does not mean he actually knows everthing! If he is reasonable he will appreciate being educated.

Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

#80108 02/28/02 07:38 PM
Joined: Feb 2002
Posts: 22
B
beach Offline OP
Member
Thank you for all the responses.

The re-inspection is tomorrow. The panel is energized but the bond from the neutral to the ges has never left the panel (and never will) reguardless of the inspector's wishes. I have had rulings over turned in the past by senior inspectors but only after I am 110% sure I was correct and didn't just interperit it differently, hence the posting in a great forum such as this.

Jon

#80109 02/28/02 08:20 PM
Joined: Nov 2001
Posts: 280
M
Member
beach
After reading your last post it help clarifies what you did. I guess I am spoiled we have some very good inspectors in my area. Since you have what you say you have then by all means there should be a bonded neutral in the sub-panel.
Can you appeal to a higher authority ? like a state inspector ?
-Mark

#80110 03/01/02 10:29 PM
Joined: Dec 2000
Posts: 4,294
Member
beach.
How did you fare? Is the inspector a little smarter?

#80111 03/01/02 10:51 PM
Joined: Feb 2002
Posts: 22
B
beach Offline OP
Member
I had a different inspector today that signed off on the project.

Thank you again.