#79735 01/20/02 09:02 PM
Joined: Oct 2000
Posts: 2,723
Likes: 1
Broom Pusher and
Member
Scott,

I could easilly see where you were going with this.
Sounds like you have been involved with Vendor coordinated project surveys too! [Linked Image] That's where I heard a few really good ones about power circuits, from the IT rep's of the Vendors.

It would take Eons to explain the maximum derated capacity of 45% to them, if the case was to run 7 - full boats [4 wire circuits].

The first thing they would say is:
"Derated Ampacity? What Planet are YOU from?"

Then the impossible task of explaining that there are 28 load [current] carrying conductors and only one non-load carrying conductor [the Equipment Ground Bonding Conductor], which will always bring up the 'ol:
"But the ""Neutral"" doesn't carry any load" debate.

I would like to hunt the joker down that started this viscious rumor and send that clown back to his / her planet of origin - or at least somewhere in deep space!

Never really installed too much of that Panduit stuff. Cable guys love it, and I guess for Voice and Data cabling it would be better than fishing down an Insulated wall [or a wall with Asbestos Impregnated Plaster / Gypsum board].

Scott SET.


Scott " 35 " Thompson
Just Say NO To Green Eggs And Ham!
Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

#79736 01/21/02 11:32 AM
Joined: Nov 2000
Posts: 2,148
R
Member
The other thing about this type of product is the plastic divider between the power and communications sections. How does this provide any shielding? When installing Cat-5 cable in the open above ceilings, we are told that the Cat-5 must be kept at least 6" away from power conductors in metal raceways and 12" from power cables without metallic jackets and 12" from fluorescent light fixtures. We are told that this separation is to avoid interference with the data transmission. In both cases I would think that the metal conduits and metal fixture would be a much better shield then the plastic divider. Why is separation required from metallic raceways, yet this little piece of plastic is ok in the wire way?
Don(resqcapt19)


Don(resqcapt19)
#79737 01/23/02 08:46 AM
Joined: Dec 2000
Posts: 4,294
Member
Don, you bring up an excellent point!
For that matter, Office Furniture presents very much the same situation. The power conductors are not shielded, but in a nonmetallic jacketed cable, and the Cat5 wiring is often run right through the same chase. EMI should run rampant.
(Maybe this raceway would cut down on the number of personal-use heaters one finds so often in offices, I should think it would generate plenty of heat)

So, do you believe that this product can be applied as advertised? I sure don't.

#79738 01/23/02 09:33 AM
Joined: Nov 2000
Posts: 2,148
R
Member
The add just says that you can install the power cables, it doesn't say that you can use them. [Linked Image]
Don(resqcapt19)


Don(resqcapt19)