Joined: Feb 2002
Posts: 14
K
Member
i have two above groud fuel tanks want 110 volt pumps will the tanks have to have a ground rod drove an egc run to each tank
thank you for any help


kenrod3020
Joined: Feb 2002
Posts: 38
H
Member
Ken

go to 515.16 NEC which will take you to 501.16 or 505.25 , first you'll have to go to 515.3 and get the right class, div , location and zone .

Joined: Feb 2002
Posts: 14
K
Member
class 1 division 1 thanks for help
after reading 505.25 the answer is no.ground
rod
Thank you high voltage

[This message has been edited by kenrod3020 (edited 03-04-2002).]


kenrod3020
Joined: Oct 2000
Posts: 2,749
Member
Please look here and get NFPA 780 for the rest of the story!

http://www.convault.com/Grounding_Instructions.pdf


Joe Tedesco, NEC Consultant