ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat
Recent Posts
Increasing demand factors in residential
by gfretwell - 03/28/24 12:43 AM
Portable generator question
by Steve Miller - 03/19/24 08:50 PM
Do we need grounding?
by NORCAL - 03/19/24 05:11 PM
240V only in a home and NEC?
by dsk - 03/19/24 06:33 AM
Cordless Tools: The Obvious Question
by renosteinke - 03/14/24 08:05 PM
New in the Gallery:
This is a new one
This is a new one
by timmp, September 24
Few pics I found
Few pics I found
by timmp, August 15
Who's Online Now
1 members (Scott35), 262 guests, and 17 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
#7943 02/28/02 11:34 PM
Joined: Aug 2001
Posts: 545
A
aldav53 Offline OP
Member
Is it legal to have a 20a 120v single recepticle outdoors "not GFI protected", for a spa if the spa has its own GFI built into the plug? Does the recept have to be 5 feet away from the spa?


The Golden Rule - "The man with the gold makes the rule"
#7944 03/01/02 10:19 AM
Joined: Mar 2001
Posts: 2,056
R
Member
I believe the only exception to GFCI protection for 120 volt receptacles in dwellings is for de-icing equipment. No one knows if someone will unplug the spa and plug in a hedge clipper at some point.

[This message has been edited by Redsy (edited 03-01-2002).]

#7945 03/02/02 02:19 AM
Joined: Feb 2002
Posts: 38
H
Member
aldav53
680 !
part VI 680.40 ,,,680.42 then in partII read 680.22(a)(4) that should be enough for ya!


Link Copied to Clipboard
Powered by UBB.threads™ PHP Forum Software 7.7.5