ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat
Recent Posts
Safety at heights?
by gfretwell - 04/23/24 03:03 PM
Old low volt E10 sockets - supplier or alternative
by gfretwell - 04/21/24 11:20 AM
Do we need grounding?
by gfretwell - 04/06/24 08:32 PM
UL 508A SPACING
by tortuga - 03/30/24 07:39 PM
Increasing demand factors in residential
by tortuga - 03/28/24 05:57 PM
New in the Gallery:
This is a new one
This is a new one
by timmp, September 24
Few pics I found
Few pics I found
by timmp, August 15
Who's Online Now
1 members (Scott35), 519 guests, and 18 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
Page 2 of 6 1 2 3 4 5 6
#79252 12/12/01 02:56 PM
Joined: Oct 2000
Posts: 4,116
Likes: 4
Member
Al,

I think if you look closely at the wire you will see that it says both THHN and THWN meaning it is approved as both.

Bill


Bill
Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

#79253 12/12/01 05:39 PM
Joined: Nov 2001
Posts: 280
M
Member
Bill:
Is Romex rated both thhn and thwn ? I know stranded wire is rated both but I think Romex is only rated for dry locations. Ergo, pvc under ground would be considered a Wet-location. No ?

#79254 12/12/01 09:50 PM
Joined: Aug 2001
Posts: 599
N
Member
Quote
THHN is allowed underground in ridgid pipe wrapped with pipe wrap, isn't this considered damp or wet location?
Where do you find that this is allowed?

#79255 12/13/01 12:22 AM
Joined: Oct 2000
Posts: 4,116
Likes: 4
Member
-T

>>Is Romex rated both thhn and thwn ? I know stranded wire is rated both but I think Romex is only rated for dry locations. Ergo, pvc under ground would be considered a Wet-location. No ?<<

You're correct. I think we're talking about 2 different things here at the same time. I was saying to Al, that, what we commonly call THHN is also (always?) labelled and rated THWN if you look at the wire. Maybe that was why He thought THHN would be allowed in conduit outside and underground.

Bill

[This message has been edited by Bill Addiss (edited 12-12-2001).]


Bill
#79256 12/13/01 08:10 AM
Joined: Mar 2001
Posts: 2,056
R
Member
Isn't it the clear plastic coating on THHN/THWN that makes the W possible in THWN?.

BTW,
Does a conduit installed above ground outdoors require wiring rated for wet locations? I say yes. Supply house man says no.

[This message has been edited by Redsy (edited 12-13-2001).]

#79257 12/13/01 09:42 AM
Joined: Oct 2000
Posts: 4,116
Likes: 4
Member
Redsy,

I don't know about the plastic covering, but I read in an NEC Handbook that the intent was that the interior of a conduit (outside) be considered a wet location. I've also heard that from a UL rep when it was brought up at a local meeting.

Bill


Bill
#79258 12/13/01 11:27 AM
Joined: Aug 2001
Posts: 545
A
aldav53 Offline OP
Member
Responding to Nick,
Why wouldn't THHN be allowed underground, if it is completely weatherproof. How else would you run circuits underground not using UF?


The Golden Rule - "The man with the gold makes the rule"
#79259 12/13/01 11:51 AM
Joined: Nov 2000
Posts: 2,236
Likes: 1
Member
THWN is allowed... And I'm betting dollars to donuts that your THHN is also marked THWN and therefore compliant...



[This message has been edited by sparky66wv (edited 12-13-2001).]


-Virgil
Residential/Commercial Inspector
5 Star Inspections
Member IAEI
#79260 12/13/01 11:52 AM
Joined: Nov 2000
Posts: 2,148
R
Member
aldav53,
There is no such thing as a dry underground conduit. You must us a wet location wire. Air moves in and out of the conduit carrying with it water vapor. When the air cools in the conduit the water vapor condenses out leaving water in the conduit. Over a period of time the conduit will fill with water.
Don(resqcapt19)


Don(resqcapt19)
#79261 12/13/01 12:57 PM
Joined: Mar 2001
Posts: 2,056
R
Member
aldav,

The whole point is, underground conduits are not weatherproof at all. The "W" is required in the designation if it is to be installed in a wet location. Look at table 310.13 and notice that all (except MI) conductors allowed in wet locations have a "W" in the (Type Letter) column.